Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Cannot create or edit bindings on TGML Graphics in a folder, "Error creating object" is shown

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Cannot create or edit bindings on TGML Graphics in a folder, "Error creating object" is shown
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Jonas_Brissman
    Jonas_Brissman
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1358 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Cannot create or edit bindings on TGML Graphics in a folder, "Error creating object" is shown

Picard Product_Support
‎2018-09-06 02:38 PM

Issue

  • It is not possible to add graphics to a folder in TAC Vista
  • The binding window can not be opened for graphics in that folder
  • When trying to add a graphic or open the binding window an error message saying “error creating object” is shown.

Environment

  • Vista 5.0 to 5.1.1 Workstation
  • I/NET gpg graphics upgraded to OGC
  • OGC graphics upgraded to TGML

Cause

The problem is that a lot of objects are created in the background when the graphic is upgraded from OGC to TGML, especially if the OGC graphic have been imported from I/NET.

The path for an object in OGC can look like this:
RGD-link54C-I/NET-54-02-02.08.AI.value.PV

The binding name in TGML after upgrading the graphic to TGML will then look like this:
WSUS11387.RGDC.I.NET.54.02.02.08.AI.value.PV

The binding name in TGML is the problem, every part of the name that is separated with a “.” will be a new object in the background, a user will not see it but it will be in the database.

In this case 10 objects are created for one binding. Note: The limitation for a folder is 32000 objects. If there are many bindings in the graphics this number will be reached pretty fast.

Resolution

Workaround: Change the “-“ sign in the path for the object in the OGC graphic to something else for example a “:”, to do this use the OGC editor, Edit-References.

Then the path will look like this:

RGD:link54C:I/NET:54:02:02.08.AI.value.PV.

You can use any character which is valid in Vista but not used when naming the objects in your database.

Now when upgrading the OGC graphic to TGML the binding name will not have dots(.) in it and only one object is created.

The problem now is that the signal path in the TGML graphic isn’t valid. So you have to use the change reference tool in TAC Vista to change it back.

From:

RGD:link54C:I/NET:54:02:02.08.AI.value.PV

To:

RGD-link54C-I/NET-54-02-02.08.AI.value.PV.

Change the “:” sign back to “-“ in the object path.

Note: This issue has been corrected in Vista 5.1.2.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 3403
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of