Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Cannot connect to Continuum database when TLS 1.0 is disabled

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Cannot connect to Continuum database when TLS 1.0 is disabled
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5172 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Cannot connect to Continuum database when TLS 1.0 is disabled

Clifton_eakes Contributor
‎2023-11-27 09:25 AM

Last Updated: ContentModerator Explorer ‎2025-09-01 03:32 AM

Issue

If TLS 1.0 is disabled on Microsoft Server 2016 you cannot connect to SQL Server 2016 database using Continuum database initialization.

Product Line

EcoStruxure Building Operation, Continuum

Environment

  • Continuum Cyberstation
  • Microsoft SQL Server 2016
  • Microsoft Server 2016.

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

Microsoft no longer supports TLS 1.0 protocol and IT departments are disabling it. The current version of the ODBC driver (SQL Server) used with Continuum will not function correctly when TLS 1.0 is disabled on Windows Server 2016 in order to use TLS 1.2. A defect/hotifx QC#2290 has been issued for this issue.

Resolution

There is a hot fix for QC#2290 that needs to be applied to the cyberstation after the installation of the ODBC driver version 13. Use the following link to download the appropriate version of the ODBC driver for your version of the OS.

Link to download ODBC driver version 13

https://www.microsoft.com/en-us/download/details.aspx?id=50420

This hotfix fixes the following defect 2290 = When TLS 1.0 is disabled on server 2016 ODBC does not connect to SQL database. Hotfix is attached below.

Contact PSS for the hotfix for Cyberstation 2.03

Please note: The ODBC Driver 13 for SQL Server needs to be installed before the hotfix is applied

Deprecation date

 

Steps to apply this hotfix:

  1. Create a ContinuumDB backup
  2. Shutdown Continuum if it is running
  3. Make a backup of OmsInst.exe in the Continuum folder
  4. Extract the OmsInst.exe from the hotfix zip file and copy the new file to the Continuum folder
  5. Do an update/initialized database
  6. Start Continuum
Labels (1)
Labels:
  • Andover Continuum
Attachments
2290_203.zip
Tags (2)
  • Find more articles tagged with:
  • AlanWood24
  • CliftonEakes23
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore