Cannot attach the Network interface to Lonmaker when Tacos is started as a service

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Cannot attach the Network interface to Lonmaker when Tacos is started as a service
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1456 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Cannot attach the Network interface to Lonmaker when Tacos is started as a service

Picard Product_Support
‎2018-09-11 01:28 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:35 AM

Issue

Cannot attach the Network interface to Lonmaker database when the Vista Server (Tacos) is started as a service. The error message is that the 'NIC interface is not connected'.

Product Line

TAC Vista

Environment

  • Echelon Lonmaker 3.1
  • Echelon Lonmaker 3.2
  • TAC Vista (all versions)

Cause

When updating Lonmaker and Vista databases as applications, it is important that Lonmaker be started first. Failure to do so can result in issues like this when Vista is reconfigured to start as a service.

Resolution

To get Vista and Lonmaker running together:

  1. Stop the Vista service and unregister it.
  2. If using a Loytec interface, set the Loytec Legacy Driver to run as a service (click the Advanced tab in LConfig).
  3. Start Lonmaker and attach the correct network interface. Ensure that Lonmaker is online.
  4. Start Vista Server as an application.
  5. From Lonmaker open the System Plugin. In the TAC Network properties, check that the correct network interface is selected. Update the Vista database.
  6. Start Vista Workstation and check that everything is online.
  7. Stop Vista and Lonmaker.
  8. Reregister Vista as a service.

For details of these operations see Registering/Unregistering TAC Vista Server as a Windows service.

Also see section 16.3 of the TAC Vista Technical Manual.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 11415
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore