Can you replace a B-Link with an Infilink200?
  • Can you replace a B-Link with an Infilink200?
  • AbeMeran
    AbeMeran
  • sesa139513
    sesa139513
  • PaulFr
    PaulFr
‎2018-09-06 10:14 AM
Last Updated: Administrator CraigEl Administrator ‎2023-05-30 06:28 PM
Are the Infilink and B-Link interchangeable or can they be converted?
Andover Continuum, EcoStruxure Building Operation
  • Infilink 200
  • B-Link
Both units are RS-485 repeaters; is there a difference?
You cannot convert from an Infilink 200 to a B-Link. They are both RS-485 repeaters, but the circuitry is slightly different to handle the electrical requirements of the BACnet MS/TP and the Infinet. You must use the correct unit for the network type you have.
The multiple ports on both repeaters (Infilink and B-Link) allow you to construct a star topology configuration, but note that devices in each spoke (port on the repeater) MUST be connected in a daisy chain topology.
Neither product contains any firmware that can be changed.