Can the Modbus RTU X Driver be used on Comm 4 of a Netcontroller II
  • Can the Modbus RTU X Driver be used on Comm 4 of a Netcontroller II
  • AdamSteele
    AdamSteele
  • PaulFr
    PaulFr
‎2018-09-10 11:48 PM
Comm4 on the NC2 is RS-422, will this operate as RS-485 if the TX & RX lines are linked?
CX9680 NCII with Modbus RTU X Driver
XDriver
Linking the TX & RX lines can cause the transmitted data to be fed back into the transmitting controller.
Yes, you can use comm 4 as a Modbus RTU X Driver to talk to 3rd party RS-485 devices.
The Netcontroller II Comm 4 is defined as an RS-485/ RS-422 port and the X Driver will close off the RX port using the RTS line while it is transmitting.
The loopback required for a 2 core screened cable is:
  • Connect TX+ to RX+
  • Connect TX- to RX-
  • Use shield connection
Note: If communications are still not able to be established, confirm that the Comm4 configuration in the Netcontroller II's web configuration page has been changed from the default RS-422 to RS-485.