Can the MP and RP VAV airflow control loop be affected by integral wind-up when the AHU is stopped
  • Can the MP and RP VAV airflow control loop be affected by integral wind-up when the AHU is stopped
  • RobertAndriolo
    RobertAndriolo
  • CraigEl
    CraigEl
Administrator CraigEl Administrator
‎2022-08-24 08:28 PM
on ‎2022-08-24 08:28 PM
Is there any adaptive tuning in the flow control loop that drives the MP-V or RP-V damper loop that will be negatively impacted by extended periods of non-zero box flow setpoints when the associated AHU is disabled (i.e. no pressure at VAV so the damper will open fully and the flow control loop will saturate).
  • Building Operation Multi-purpose VAV
  • EasyLogic RP-V
No information on the internal Variable Air Volume Data object
Airflow control in the MP and RP VAV controllers is not impacted by extended periods of non-zero box flow setpoints when the associated AHU is disabled. The damper is actuated by a single-speed motor with three states (open, close, hold), and to avoid windup or saturation effects, the flow control algorithm is not a PID loop. There is no need to link the AHU enable to the MP or RP flow control logic.
  • CraigEllis22