Can the MNL 20RF be used in a Master / Slave configuration?
  • Can the MNL 20RF be used in a Master / Slave configuration?
  • sesa125819
    sesa125819
‎2018-09-06 01:59 PM
Controllers that will operate in a  Master / Slave configuration, where values such as the setpoint, temperature etc can be shared.
MNL controllers
LonMaker
WorkPlace Tech
Configuration issue.
The MNL 20RF controllers will not directly act in a Master / Slave configuration.
If there is a requirement to share values between controllers, such as the setpoint, temperature etc. then these values need to be assigned to SNVT's in each controller, and the controllers bound together using LonMaker or similar.
  • TAC IA Series
  • 4849
This is a heading