Can the MF41-6043 actuator work with the DMS MicroSmart MSC-V-511 controller?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Can the MF41-6043 actuator work with the DMS MicroSmart MSC-V-511 controller?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • JohnBoehmer
    JohnBoehmer
  • Leo_Tantalo
    Leo_Tantalo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3329 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Can the MF41-6043 actuator work with the DMS MicroSmart MSC-V-511 controller?

Picard Product_Support
‎2018-09-11 05:59 AM

Issue

The customer is replacing a defective actuator on a hot water reheat valve downstream of a VAV box.  The VAV and associated hot water valve are controlled by a DMS MicroSmart MSC-V-511 controller.

Can the MF41-6043 actuator be wired into the MSC-V-511 and control the valve?

Environment

DMS

MSC-V-511

MF41-6043

Cause

Defective actuator is discontinued and cannot be swapped with an identical, working one.

Resolution

The triac outputs on the MSC-V-511 can properly control the MF41-6043 actuator.

  • Terminals D1 to D4 provide 24 Vac which is the voltage required for the actuator.
  • Look at the MSC-V-511 installation guide (F-25710) on page 18 for details on how to wire and program the actuator.
  • Remember that the MSC-V-511 provides 24 Vac power so there's no need for an external power source.
     
  • If needed, the MF41-6043 installation guide has wiring diagrams on page 6.
  • The actuator requires 2.3 VA. The digital outputs on the MSC-V-511 can provide up to 12 VA.
Labels (2)
Labels:
  • Field Devices
  • TAC IA Series
Attachments
Tags (1)
  • Find more articles tagged with:
  • 14303
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore