Can the DUIC-5P-12V digital point card be used on a MNL-200?
  • Can the DUIC-5P-12V digital point card be used on a MNL-200?
  • CraigEl
    CraigEl
  • sesa116873_brid
    sesa116873_brid
‎2018-09-06 01:32 PM
Last Updated: Administrator CraigEl Administrator ‎2023-12-06 03:07 PM
TAC IA Series
IA Series MNL-200
Integration of multiple status inputs
The DUIC-5P-12V will function with the MNL-200 controller.
  1. Do not use the BACnet DUI_Application.
  2. Use the WorkPlace Tech's DUI Expander object instead.
  3. Also, remove the JP1 jumper on the DUIC-5P-12V board.
  • TAC IA Series
Tags (2)
  • 5694
  • CraigEllis23