Can an Infinity Controller with a Modbus xdriver operate as a slave node to a third party Modbus device that is set up as the master node?
  • Can an Infinity Controller with a Modbus xdriver operate as a slave node to a third party Modbus device that is set up as the...
  • JohnBoehmer
    JohnBoehmer
‎2018-09-06 11:02 AM
Modbus RTU
Modbus TCP/IP
xdriver
Third party modbus Master has to poll data from a CX or BCX controller that is set up as a slave node.
The Modbus TCP/IP xdriver can be configured to operate as a slave node.
The Modbus RTU xdriver must be the Master node whatever MODbus network it is attached to.
  • 11359