Want to be able to set up a user account where the user can reload controllers, but cannot edit or delete them.
CyberStation
Do not want certain users to be able to edit or delete controllers.
When testing this with v1.93 it appears you have to give the user "View" and "Edit" access to the InfinityController object type in the security editor application if you want them to be able to reload from ContinuumExplorer. You can lock all the other attributes including the tabs.
You can even lock "View" and let them open a Listview of controllers and reload from there - then they don't see the objects within the controllers either.