Can Continuum Engineering Units be changed and/or added to?
  • Can Continuum Engineering Units be changed and/or added to?
  • AdamSteele
    AdamSteele
‎2018-09-10 10:03 PM
Continuum Cyberstation
Continuum Infinity Controllers
Continuum BACnet Controllers
Want to change or add an Engineering Unit as the unit I require is not present.
Engineering Units are handled differently depending on the type of controller being used.
Infinity Controllers are able to have there units defined to be whatever you want (defined as up to 12 digits of text) in the Units field of the Input or Output object.
BACnet Controllers Input and Output Units are predefined by the BACnet specification and are chosen from a set list of Engineering Units. These cannot be changed or added to.