Users want to know if the BACnet object_name property for an I/A Series R2 or G3 station can be modified.
TAC IA Series
  • I/A Series R2 UNC-410
  • I/A Series R2 UNC-520
  • I/A Series G3 ENC-410
  • I/A Series G3 ENC-520
The BACnet object_name is automatically generated by the system using:
  • The station name
  • The assigned BACnet device instance number
For example:
  • Station name: BldgA
  • Device instance: 500
  • Resulting object_name: BldgA_500
This behavior is hardcoded and cannot be overridden.
The BACnet object_name cannot be changed by the user.
  • To influence the object_name, you must rename the station or change the BACnet device instance number.
  • There is no direct property or setting to manually edit the object_name.