CSC - Help with checking the operation of this controller.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • CSC - Help with checking the operation of this controller.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2239 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

CSC - Help with checking the operation of this controller.

Picard Product_Support
‎2018-09-10 03:34 AM

Last Updated: Crewman ContentModerator ‎2025-10-10 02:54 AM

Issue

Checking operation of CSC.

Product Line

Field Devices

Environment

  • CSC5252
  • CSC5352

Cause

The operation of the CSC compensator explanation.

Resolution

The operation of a compensator is to adjust the system flow temperature, in relation to changes in the outside air temperature. The system flow temperature can be further adjusted by the addition of a room temperature sensor, which will provide room influence.

The CSC 5252/5352 controller is programmed with a complete set of "Default" settings, these settings will allow the controller to operate as soon as its powered up.

Although the controller has a complete range of adjustable settings, accessed through the "Fine Tune Mode", for a basic installation the "Quick Set Mode" can be used. The screen shot below explains how to enter the Quick Set Mode and the settings available.

Controller data sheet

Controller User guide

 

Compensated Flow Temperature Set-point:

The compensated flow temperature set-point is automatically adjusted based on a ratio for set-point adjustments against the outside temperature changes.

A consistent ratio across the entire outside temperature range, may not provide suitable control.
For example: with radiator type systems, radiators are less efficient at lower water flow temperatures and need to be provided with a higher temperature to compensate for this initially.

The “Set compensator ratio 1”and the “Set Ratio 2” settings provide the ratio of the change to the flow temperature set-point for changes in the outside air temperature, the ratio used is based on the “Set Change-over Value”, with the compensated slope starting from the “Set Flow Origin”.
The “Set Flow Temperature Set-up Value” and “Set Night Set Back Value” provide a constant adjustment of the flow temperature set-point to a given building control requirement.

The default settings would give a resultant flow temperature as shown follows:

 

Image 1.jpg

 

The CSC5352 Calculator presents these settings in a graphical and listed format, making it easier to visually confirm the effects any changes to these settings would make.

 

 

Labels (1)
Labels:
  • Field Devices
Attachments
Tags (2)
  • Find more articles tagged with:
  • 6296
  • GaryMontague21
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore