Issue
Communication failures occur when connecting a MicroNet ARCnet system via a MicroNet Manager Interface (MNMI) to Xenta 555/731, VisiSat, or SBO servers.
Product Line
Satchwell MicroNet, TAC Vista, EcoStruxure Building Operation
Environment
- Xenta 555 or Xenta 731 communicating to a MicroNet ARCnet LAN
- VisiSat communicating to a MicroNet ARCnet LAN
- Building Operations Server communicating to a MicroNet ARCnet LAN
Cause
Incorrect bit switch configuration on the MicroNet MI interface.
Resolution
Cold Starting the MicroNet MI
⚠️ Caution: This procedure will erase all configuration data from the device’s EEPROM and restore factory defaults.
Steps:
-
Power On the Device
- Ensure the RUN LED flashes approximately once per second.
-
Disconnect Communication Ports
- Unplug any connections to 9-pin plug 3 and 9-pin plug 4.
- Unplug any connections to 9-pin plug 3 and 9-pin plug 4.
-
Reset Switches
- Set all bit switches (S1) to the OFF position.
- Set all bit switches (S1) to the OFF position.
-
Initiate Cold Start
- Toggle bit switch 8 ON, then OFF.
- No visible change will occur at this stage.
- Toggle bit switch 8 ON, then OFF.
-
Configure for Xenta 555 Direct Connection
- Set only switch 1 to ON; all others must remain OFF.
- Toggle bit switch 8 ON, then OFF again.
- Set only switch 1 to ON; all others must remain OFF.
-
Verify LEDs
- RUN, WINK, and MODEM LEDs should light up for ~1.5 seconds.
- RUN LED should resume flashing once per second.
🔍 Note: This cold-start procedure differs from that of a controller, which only requires toggling switch 8. Refer to data sheet DS10217A for detailed specifications.