Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Best practice on adding reference host and creating routing table

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Best practice on adding reference host and creating routing table
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • sesa145087_brid
    sesa145087_brid
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1658 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Best practice on adding reference host and creating routing table

Picard Product_Support
‎2018-09-11 01:42 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:36 PM

Issue

Host conflict window always pops up, and cleaning routing table doesn't help.

Product Line

EcoStruxure Building Operation, TAC INET

Environment

I/NET

Cause

Host conflict is a normal issue happening in I/NET. It is usually caused by the duplicated host ID setting on different servers, or an engineer laptop is inserted into the network with the same host ID setting with some server. And the routing table will be messed up since all the IP related information will be recorded in the routing table and it will be distributed to all the network devices, including all the servers and NPRs. The usual solution is to clear all the routing tables on all the network devices, . Refer to How to Remove the Routing Tables in a Device or PC about how to clear the routing tables.

But if the routing table is cross referred, like Server 1 adding NPR 1 and NPR 2 as reference hosts, while NPR1 adding Server 1 and NPR 2 as reference host, the routing table will never be cleaned out since when you clean the routing table for Server 1, NPR1 and NPR 2 will still try to send their wrong routing table to Server 1. Unless all the network devices are disconnected and the routing tables are cleaned one by one, or disable the 50069 port for the whole network, which is used by the communication between network devices, there is no other way to clean them out. And these two method are not applicable sometimes.

Resolution

If the routing table can be managed well, such kind of issue will never happen. The best practice on adding reference host and creating routing table is:

  1. On the servers: Choose one server as the master reference host. All the other servers add this server as reference host. Don't add NPR as reference host. All the NPRs can be added into the master server by clicking on the NPR button in I/NET configuration and added one by one manually. By this way, the master server can build its own routing table without impacted by other devices. And this one is the only routing table in the whole network.
  2. On NPRs. If NPR doesn't need to talk to other NPRs, like transferring indirect points, there is no need to add reference host for NPR. If indirect points are needed, just add the master server as the reference host. Then this NPR will be able to see all the other NPRs based on the routing table on the master server.
  3. If the master server is not equipped with UPS, or not always promises to be online, another master NPR can be chosen as a secondary reference host. Add this NPR as a reference host to all the servers and other NPRs.

Under this scenario. if the routing table needs to be cleaned, only the master server and the secondary reference host need to be cleaned. It will be more easier to clean all the routing table and get rid of the host conflict error.

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 17123
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore