Backup and Restore Process for Building Operation WebReports

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Backup and Restore Process for Building Operation WebReports
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • Derrick_Ratliff
    Derrick_Ratliff
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2431 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Backup and Restore Process for Building Operation WebReports

Picard Product_Support
‎2020-09-08 06:52 PM

Issue

Backup and Restore Process for WebReports

Product Line

EcoStruxure Building Operation

Environment

  • WebReports
  • Reports Server
  • SQL Server 2008 R2

Cause

Need detailed backup process

Resolution

Refer to Online Help Topic for details


Backing Up the WebReports Database 

  1. On the Windows toolbar, select Start, and then click SQL Server Management Studio.
  2. Click Connect.
     
    Note: When using a remote computer to connect to the Report Server SQL database, the Windows Accounts must exist on both machines and have administrative rights for the SQL database otherwise a successful backup will not occur.  In this instance, it is recommended to use the SysAdmin 'sa' login / password details when connecting in remotely.
     
  3. Expand the Databases folder.
  4. Right-click StruxureWareReportsDB, point to Tasks, then click Back Up.
  5. Under Destination, click Add.
  6. Click OK.
  7. In the Destination on disk box, select the backup destination.
  8. Click OK.
  9. Click OK.

 

Restoring the WebReports Database

  1. Ensure the Enterprise Server is up and running with the correct database. 
  2. Stop the SQL Server Reporting Services and WebReports Agent (if installed). 
    Note: If moving the WebReports Database it is recommended to restore the database then Install WebReports.  Then when Installing WebReports select Upgrade existing (as shown) and NOT New database 
    WebReports_UpgradeDB.png
  3. Restore the WebReports database to recover reports data from backup.  This will include any Dashboard reports saved.
  4. On the Windows toolbar, select Start, and then click SQL Server Management Studio.
  5. Click Connect.
  6. Expand the Databases folder.
  7. Right-click StruxureWareReportsDB and select Tasks, then select Restore, then select Database.
  8. In the Restore Database dialog box, select the database set(s) that you want to restore.
  9. Click OK.
  10. Click OK.
  11. If not already installed now complete the installation of WebReports 
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • 12462
  • RobertAndriolo20
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore