BCX reload error "Infinity controller error: Controller has no assigned Infinet port"

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BCX reload error "Infinity controller error: Controller has no assigned Infinet port"
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • GavinHe
    GavinHe
  • Product_Support
    Product_Support
  • Carl_Slack
    Carl_Slack

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4793 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BCX reload error "Infinity controller error: Controller has no assigned Infinet port"

Picard Product_Support
‎2018-09-06 02:15 PM

Last Updated: Sisko GavinHe Sisko ‎2022-08-25 09:12 AM

Issue

Reload of BCX receives error "Infinity controller error: Controller has no assigned Infinet port An error was detected while attempting to set an attribute in a remote Infinity object"

Product Line

Andover Continuum

Environment

  • Continuum Cyberstation
  • BCX 9640
  • BCX4040
  • Infinet controller
  • b3

Cause

Reloading of a BCX 9640 resulted in error "Infinity controller error: Controller has no assigned Infinet port.  An error was detected while attempting to set an attribute in a remote Infinity object"

 

Suspected that a learn on the commport was performed or infinet controllers were manually created causing no assigned comm port.

Resolution

As with any edit of the Continuum system, please make sure to backup the database.

 

Follow these steps:

  1. Send BCX to text file 
  2. Add commport to each Infinet controller entry as below
  3. Import newly edited text dump file into the BCX.
  4. Reload BCX

 

Example of an original dump file exported in step 1 and the new dump file after the commport is added in step 2.

Original Dump File New Dump File
Object : Spare
  Type : InfinityInfinetCtlr
  LastChange : 1/11/2011 4:01:19 PM
  DeviceId : Zoo\GreenHouse
  Alias : Spare
  CreateTime : 8/24/2010 8:28:22 AM
  CreatedBy : Root\Acc
  TimeLocked : 2/15/2011 12:53:26 PM
  InstanceId : 7015/7167
  CntrlType : 851
  Description : Spare Controller No Points
  InfinetId : 1
  Location : Control Cabinet
  NetworkId : 11
  SerialNum : 12345
  VersionNum : 2.160000
 EndObject

 

Object : Spare
  Type : InfinityInfinetCtlr
  LastChange : 1/11/2011 4:01:19 PM
  DeviceId : Zoo\GreenHouse
  Alias : Spare
  CreateTime : 8/24/2010 8:28:22 AM
  CreatedBy : Root\Acc
  TimeLocked : 2/15/2011 12:53:26 PM
  InstanceId : 7015/7167
  CntrlType : 851
  Description : Spare Controller No Points
  InfinetId : 1
  Location : Control Cabinet
  NetworkId : 11
  Port : comm2
  SerialNum : 12345
  VersionNum : 2.160000
 EndObject

 

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 4382
  • GavinHeward22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore