Issue
Reload of BCX receives error "Infinity controller error: Controller has no assigned Infinet port An error was detected while attempting to set an attribute in a remote Infinity object"
Product Line
Andover Continuum
Environment
- Continuum Cyberstation
- BCX 9640
- BCX4040
- Infinet controller
- b3
Cause
Reloading of a BCX 9640 resulted in error "Infinity controller error: Controller has no assigned Infinet port. An error was detected while attempting to set an attribute in a remote Infinity object"
Suspected that a learn on the commport was performed or infinet controllers were manually created causing no assigned comm port.
Resolution
As with any edit of the Continuum system, please make sure to backup the database.
Follow these steps:
- Send BCX to text file
- Add commport to each Infinet controller entry as below
- Import newly edited text dump file into the BCX.
- Reload BCX
Example of an original dump file exported in step 1 and the new dump file after the commport is added in step 2.
Original Dump File | New Dump File |
Object : Spare Type : InfinityInfinetCtlr LastChange : 1/11/2011 4:01:19 PM DeviceId : Zoo\GreenHouse Alias : Spare CreateTime : 8/24/2010 8:28:22 AM CreatedBy : Root\Acc TimeLocked : 2/15/2011 12:53:26 PM InstanceId : 7015/7167 CntrlType : 851 Description : Spare Controller No Points InfinetId : 1 Location : Control Cabinet NetworkId : 11 SerialNum : 12345 VersionNum : 2.160000 EndObject |
Object : Spare |