Continuum has a limit on the number of entries that can be added to the BBMD table in the bCX and CyberStation.
Do the AS and ES servers have the same limitation?
  • Building Operation Automation Server (AS-P, AS-B)
  • Continuum
Limitations must be known for engineering design.
The number of BDT Entries you can add to the BBMD table in EcoStruxure Building Operation is limited only by the available resources, so for all practical purpose there is no limit.
Device
BDT (Broadcast Distribution Table)
FDT (Foreign Device Table)
ES
only limited by memory
64 (up to v1.4) 600 (from v1.5)
AS
64 (up to v1.4) 254 (from v1.5)
ASB
50
bCX1
32
32
Cyberstation
1024
1024
Always refer to the Architectural Guidelines for the latest information