Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

BAS2800+ - MultiTech MT5656 serial modem codes.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BAS2800+ - MultiTech MT5656 serial modem codes.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidChild
    DavidChild
  • sesa139513
    sesa139513
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1723 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BAS2800+ - MultiTech MT5656 serial modem codes.

Picard Product_Support
‎2018-09-06 09:43 AM

Last Updated: Sisko DavidChild Sisko ‎2021-01-29 09:07 AM

Issue

MultiTech MT5656 serial modem codes.

Product Line

Satchwell BAS2800+

Environment

  • MultiTech
  • Modem

Cause

The MultiTech MT5600 is no longer available and is replace by the MT5656.

Resolution

The Multitech MT5600 modem has been made obsolete and has been replaced by the MT5656. We have experienced communication problems when mixing these two models of modem.

It has been found that the most consistent and reliable AT codes for the Multitech MT5656 modem when communicating with an MT5600 modem connected at the BAS 2800+ front end are:-

AT&F0

ATS0=1

ATE1

AT\N5

AT%C0

AT+MS=V34,1,300,9600,300,9600

AT&K0

ATQ0

AT%E2

ATX4

AT&D3

ATM0

AT&W0

AT&W1

Note:

If any of the remote sites are using an MT5600 modem then the BAS 2800+ front end modem should always be an MT5600. If a replacement modem is required at the front end then it is recommended that one of the remote sites MT5600 modem is replaced with an MT5656 modem. This will release the MT5600 modem for front end duty.

If the whole installation consists of MT5656 modems only, there are no known communications issues.

When manually connecting from either front end or remote site a connection was established successfully every time.

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 15548
  • multi-tech
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of