BAS & Sigma - Minutes to next switch is a large number.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BAS & Sigma - Minutes to next switch is a large number.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidChild
    DavidChild
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
982 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BAS & Sigma - Minutes to next switch is a large number.

Picard Product_Support
‎2018-09-10 12:03 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-22 12:14 AM

Issue

When viewing an optimiser point, the value for “Minutes to Next Switch” appears unusually large.

Product Line

Satchwell BAS & Sigma

Environment

  • Satchwell BAS
  • Satchwell Sigma

Cause

The optimiser is unable to accurately calculate the time to the next switch due to one or more of the following reasons:

  • The associated time schedule is in a “Manual” condition.
  • The optimiser point is correctly cross-referenced to a time schedule, but that schedule is further cross-referenced to another point (e.g., a programmable point) via:
    • Low Action (LA)
    • High Action (HA)
    • Holiday point that is not correctly configured as a holiday schedule.

This misconfiguration prevents the optimiser from determining the next switch time, resulting in a default large value.

Resolution

To resolve this issue, review and adjust the hierarchy of overrides and actions in the software. The goal is to ensure the optimiser can directly interpret the time schedule without unnecessary layers of overrides.

Recommended Configuration Examples

Example 1

Instead of:

Holiday > Overrides (e.g., Programmable Points) > Time Schedule > Optimiser > Plant Level

Use:

Holiday > Time Schedule > Optimiser > Overrides (e.g., Programmable Points) > Plant Level

Example 2

Instead of:

Overrides (e.g., Programmable Points) > HA or LA xref > Time Schedule > Optimiser > Plant Level

Use:

Time Schedule > Optimiser > Overrides (e.g., Programmable Points) > Plant Level

Additional Notes

  • Ensure that holiday schedules are correctly defined as holiday points.
  • Avoid placing overrides or programmable actions above the optimiser in the control hierarchy.
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 5581
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore