Issue
“BACnet Read Property Multiple Error” followed by a property name and device or object name.
Product Line
TAC IA SeriesEnvironment
I/A Series R2 (Niagara) UNC or BACnet Server
Cause
The station attempts to use this function for efficiency, but when unsupported, the device responds with an error.
Resolution
- This is normal operation and does not indicate a failure.
- All requested data will still be retrieved because the station automatically falls back to polling each property individually.
- To suppress the warning messages:
- Set the device’s Read Property Multiple property to false in the configuration.
- Note: Disabling Read Property Multiple will slow down polling for that device.