What is the BACnet Network ID - UDP
Andover Continuum
  • Continuum BACnet
  • bCX4000
  • bCX4040
Documentation
The BACnet Network ID - UDP identifies the BACnet IP network that the bCX controller communicates on, it is 1 by default.  The BACnet Network ID - UDP should be the same for all bCX controllers that need to communicate on the BACnet IP network.  Consult UDP setting in bCX40x0 have been set to different values for additional information.
Note: - CyberStation does not have a setting for BACnet Network ID - UDP.   CyberStation will communicate with all ethernet level BACnet devices regardless of the network they sit on.