BACnet Interface has unresolved references
  • BACnet Interface has unresolved references
  • RandyDavis
    RandyDavis
  • JonGreen
    JonGreen
Commander JonGreen Commander
‎2020-09-09 12:06 PM
on ‎2020-09-09 12:06 PM
BACnet Interface has "!" with unresolved references
  • Building Operation Automation Server v2.0 or later
  • Building Operation Multi-purpose VAV
  • Building Operation Multi-purpose Controller
During the startup of a Smart-X controller, the auto-association feature fails and the data becomes corrupted
  1. Go to BACnet Interface -> Time Sync Recipients
  2. Find any devices listed as DEVICE_<Instance ID>, select & delete
  3. Verify all devices listed are configured as follows:
  4. SmartX controllers
  5. Recipient Type: Reference
  6. Recipient Device Object Reference: <Device in System Tree>
  7. If Recipient Name does not match, copy from Object Reference and paste in the field. This helps humans troubleshoot the issue.
  8. DO NOT set Recipient Type = MAC Address, Network ID = Global Network or Local Network, Mac Address = Broadcast. This will set time on other ES/AS with BACnet Interface on the BACnet System.
  • JonGreen20
50% helpful (1/2)