Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

BACnet Interface - Contains Unresolved BACnet Reference

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BACnet Interface - Contains Unresolved BACnet Reference
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • Jonathan
    Jonathan
  • David_Purser
    David_Purser

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
3 Likes
10436 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BACnet Interface - Contains Unresolved BACnet Reference

Administrator Jonathan Administrator
‎2020-01-16 08:37 AM

Last Updated: Guinan RandyDavis Guinan ‎2022-09-29 11:03 AM

Issue

The BACnet Interface Contains a Yellow Exclamation Icon and when you hover over to read the tooltip it states, “Contains Unresolved BACnet Reference”.

Yellow Bang on the BACnet Interface.JPG

Product Line

EcoStruxure Building Operation

Environment

  • EcoStruxure Building Operation
  • Building Operation Multi-Purpose Controller
  • Building Operation Multi-purpose VAV
  • Building Operation Room Controller
  • Building Operation IP-IO

Cause

There is a reference misconfiguration within the “Time Synchronization Recipients” under the BACnet Interface.

Resolution

  1. Select and highlight the BACnet Interface then select the Time Synchronization Recipients TABTime Sync Recipients-Screen 1.JPG
  2. Compare the list Names with the list to the left under the IP Network Tree. In this example, we can see that MPV-9A is not a controller within my database under the IP Network_2.
  3. Highlight/Select the controller under Time Synchronization recipients and edit the details by clicking on the pencil icon.
    Time Sync Recipients-Screen 2.JPG
  4. Within the Time Synchronization Recipient screen, we want to adjust this device to match the ACTUAL device located under our IP Network_2 named MP-9A_Roof.
  5. Click on the “three dots|ellipsis “to browse to the correct Recipient device identifier.
  6. In this example: Select the BACnet Interface > IP Network_2 > MPV-9A_Roof as this is the correct path for this device.Time Sync Recipients-Screen 3.JPG
  7. At this point, we have the correct path under the Recipient device object reference.
  8. Adjust the Recipient name to match the BACnet name you configured for that device. In this example, it was set to MPV-9A_Roof. TIP: Click the BACnet button to fill in the recipient name field with the BACnet name of the device referenced in the recipient device object reference field.
  9. Click OK.Time Sync Recipients-Screen 4.JPG
  10. If this is the only device you need to modify then you can click the SAVE icon. If you have more devices to adjust, then you will repeat the process until you're done with all the devices.Time Sync Recipients-Screen 5.JPG
  11. You have now resolved the reference errors against the BACnet Interface.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • DavidPurser22
  • JonathanHernandez20
Was this article helpful? Yes No
90% helpful (17/19)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of