BACnet Flow Balance Tool – Accessing Updated K-Factor Post-Balancing

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BACnet Flow Balance Tool – Accessing Updated K-Factor Post-Balancing
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
8815 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BACnet Flow Balance Tool – Accessing Updated K-Factor Post-Balancing

Picard Product_Support
‎2018-09-11 12:54 PM

Last Updated: Administrator CraigEl Administrator ‎2025-09-29 09:48 PM

Issue

In the LON Flow Balance program the k-factor calculated by the balance process can be displayed at the end of the procedure.  I cannot determine how to read it in the BACnet Flow Balance program.  The value is needed so that the application file can be updated so that if the controller needs to be re-downloaded, it will not need to be balanced again.

Product Line

TAC IA Series

Environment

  • BACnet  MNB-V1 or MNB-V2 controller
  • WorkPlace Tech Tool software release 5.7.2 or newer (Optional, for backup)

Cause

The BACnet Flow Balance process uses a procedure that results in a more accurate flow calibration process. As a result of this process the rated box flow value does not get re-calculated during the balance process.

Resolution

The BACnet MNB-V1 & MNB-V2 controllers store Flow Balance calibration data separately from the application file. This ensures that a revised application can be downloaded without losing air balance calibration data.

To access the updated k-factor:

  1. Navigate to the Flow Balance Data screen
    • Click “Balance Data” in the left menu of the Flow Balance screen.
    • This screen displays all data entered and generated during the balance process.
  2. Refer to Documentation

    • See the figure “Flow Balance Reporting – Flow Balance Details” in Chapter 5 of the MicroNet BACnet Commissioning Tool / Flow Balance Users Guide (F-27358).

  3. Generate Reports

    • Both the BACnet Flow Balance program and WorkPlace Commissioning Tool can generate flow balance reports for individual or multiple BACnet VAV controllers.

    • Reports are automatically saved and can be viewed/printed in HTML format without reopening the tool.

  4. Backup and Restore Functionality

    • WorkPlace Tech Tool 5.7.2 introduced a feature to back up the complete application, including:

      • COV subscription data

      • Flow balance calibration data

    • If a controller is replaced, use the WorkPlace Commissioning Tool to restore the backup.

    • Refer to the WorkPlace Tech Commissioning Tool Backup and Restore section on page 10 of the release notes (F-27526-3) for details.

Additional Resources

  • WorkPlace Tech Tool 5.7.2 Release Notes (F-27526-3)
Labels (1)
Labels:
  • TAC IA Series
Attachments
Tags (2)
  • Find more articles tagged with:
  • 7315
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore