Automation Server independent of Enterprise Server
  • Automation Server independent of Enterprise Server
  • sesa139513
    sesa139513
  • CraigEl
    CraigEl
‎2018-09-10 07:40 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-09 07:24 PM
Can the AS, work independently or together without an ES?
StruxureWare Building Operation site, any version
Are bindings or other communication between two AS possible if there is no ES?
The AS, is designed to work independently or in conjunction with others, or in conjunction with an ES.
Points, Bindings, Schedules, etc. can be setup on the AS using the Workstation. With the ES service stopped, the Points, Bindings, etc. on the AS continue to reflect the values on themselves or if the Bindings interlink between multiple AS.
For multiple AS configuration check the AS are listed in the Communication tab of each other. From your workstation highlight the AS and the tabs shown are List View, Device Discovery, Date & Time, Communication, and Properties. Under Communication the other AS devices should be listed as well as the ES.
For information on a Automation Server alone at a site and licensing requirements, see License requirements for AS alone at a site