Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Automation Server Trend log does not record at time interval when stopped by power cycle

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Automation Server Trend log does not record at time interval when stopped by power cycle
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • SangKim
    SangKim
  • LeeCravens
    LeeCravens
  • AbeMeran
    AbeMeran

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2518 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Automation Server Trend log does not record at time interval when stopped by power cycle

Picard Product_Support
‎2018-09-06 11:42 AM

Issue

Automation Server -Trend does not record at time interval when it is stopped and restarted by AS power cycle or reboot.

Trend log cycle is thrown off when the trend is stopped and started again due to an AS power cycle or reboot. For example, an Interval Trend Log set up to log ever 15 minutes with an activation time right on the hour (1:00, 1:15, 1:30 etc.) that lost power for a while would start logging as soon as the power was restored (this might be 2:07, 2:22, 2:37 etc. for example).

UPDATE:

This issue has been corrected in SBO version 1.5, any SBO version 1.5 or grater will synchronize the interval log to the clock.

Product Line

EcoStruxure Building Operation

Environment

  • Automation Server
  • Struxureware Workstation

Cause

This is how Interval Trends behave. For interval trending based on the time a different approach must be taken.

UPDATE:

This issue has been corrected in SBO version 1.5, any SBO version 1.5 or grater will synchronize the interval log to the clock.

Resolution

Rather than using Interval Trend Logs use Variable Triggered Trend Logs and trigger them using the following method:

  1. Create a new binary value and a new function block program. The value will serve to trigger the Variable Triggered Trend Logs. The program will set the trigger variable based on a certain time interval (for example on the hour, 15 minutes, 30 minutes and 45 minutes).
  2. Edit the program and configure it as seen in the image below. This include an integer input, an expression that will evaluate the minutes attribute of the AS and a binary output. You can also download an export of the program and value here.
  3. Bind the input of the program to the minutes attribute of the Automation Server and the output to the trigger value that you created. Note that you should also bind the Task to Task 1 (100 ms) for best performance.
  4. Create your Variable Triggered Trend Logs on the points that you want to trend. Do this by right-clicking the point to trend and selecting New > Trend and then in the dialog select Variable Triggered Trend Log.
  5. Click Next and then set the Trigger Variable to the value that you created. Make sure Trigger when is set to Change to true.

Note that this example will create a log at 0, 15, 30 and 45 minutes past the hour. You can modify the program to trigger only every hour, every half hour or however you want.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
15 Minute Trend Log Trigger Export.zip
Tags (4)
  • Find more articles tagged with:
  • 11049
  • stamp
  • timestamp
  • trendlog
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now