Automatic Window Control

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Automatic Window Control
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • DavidChild
    DavidChild
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2352 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Automatic Window Control

Picard Product_Support
‎2018-09-11 04:02 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-07 06:19 PM

Issue

How to program software for automatic window modulation using BAS or Sigma.

Product Line

Satchwell BAS & Sigma

Environment

Satchwell BAS & Sigma

Cause

Standard window operations typically support only open/close functionality. However, in this case, the requirement is for staged modulation—windows should open or close in increments based on environmental conditions and manual overrides.

Resolution

To enable modulated control of windows (rather than simple open/close), the following setup is required:

1. Window Travel Time

  • Determine the total time for the window to move from fully closed to fully open.
  • Ensure symmetry: open and close times must be equal for accurate modulation.

2. Control Strategy

  • Modulation is achieved in fixed stages (e.g., 25%, 50%, 75%, 100%).
  • This allows granular control of ventilation and environmental conditions.

3. Override Functionality

  • The system should allow manual override by the classroom teacher to open or close windows as needed.

4. Environmental Interlocks

  • Integrate interlocks for wind direction and rain detection to ensure safe operation.
  • These interlocks prevent window operation under adverse weather conditions.

Implementation Example

A sample configuration for a classroom includes all necessary objects and logic.

Inputs

  • P60 = Time schedule
  • P15 = Fire
  • P16 = Rain
  • P17 = Teacher Override On
  • P18 = Teacher Override Off
  • P19 = Wind Direction
  • P35 = Temperature control loop (set to Pb only)
  • P34 = CO₂ control loop (set to Pb only)
  • P33 = Calculation point (set to maximum of P34 and P35)

Programmable Points


P36 – CONTROL SLOW RAMP
Tracks the max temp/CO₂ signal and ramps slowly.
Timer must exceed window pulse timer.
Also tracks overrides to resume control from the correct point.

10 XFlo = POINT 0|33
20 IF TIME LEFT THEN GOTO 50
30 IF XFlo > YFlo THEN YFlo = YFlo + 1.00000
40 IF XFlo < YFlo THEN YFlo = YFlo - 1.00000
50 IF YFlo CHANGED THEN SET TIMER 10
60 IF POINT 0|18 CLOSED THEN YFlo = 0.000000
70 IF POINT 0|15 CLOSED THEN YFlo = 0.000000
80 IF POINT 0|16 CLOSED THEN YFlo = 0.000000
90 IF POINT 0|19 CLOSED THEN YFlo = 0.000000
100 IF POINT 0|60 CLOSED THEN YFlo = 0.000000
110 IF POINT 0|17 CLOSED THEN YFlo = 100.000
120 RETURN VIA TEXT 92 VALUE YFlo​

P37 – CONTROL 10% INTERVAL
Divides control loop into 10 stages.

10 XFlo = POINT 0|36
20 IF XFlo = 100.000 THEN YFlo = 100.000
30 IF XFlo < 100.000 THEN YFlo = 90.0000
40 IF XFlo < 90.0000 THEN YFlo = 80.0000
50 IF XFlo < 80.0000 THEN YFlo = 70.0000
60 IF XFlo < 70.0000 THEN YFlo = 60.0000
70 IF XFlo < 60.0000 THEN YFlo = 50.0000
80 IF XFlo < 50.0000 THEN YFlo = 40.0000
90 IF XFlo < 40.0000 THEN YFlo = 30.0000
100 IF XFlo < 30.0000 THEN YFlo = 20.0000
110 IF XFlo < 20.0000 THEN YFlo = 10.0000
120 IF XFlo < 10.0000 THEN YFlo = 0.000000
130 RETURN VIA TEXT 92 VALUE YFlo​

P38 – OPEN CONTROL
Xref your Window Open DO to this point.
Timer = 72s / 10 stages = 7s per stage.

10 XFlo = POINT 0|37
20 IF XFlo UP THEN SET TIMER 7
30 IF POINT 0|18 CLOSED THEN RETURN FALSE "TchO/R Close"
40 IF POINT 0|15 CLOSED THEN RETURN FALSE "FIRE"
50 IF POINT 0|16 CLOSED THEN RETURN FALSE "RAIN"
60 IF POINT 0|19 CLOSED THEN RETURN FALSE "WrgWind Dir'"
70 IF POINT 0|60 CLOSED THEN RETURN FALSE "Time Off"
80 IF POINT 0|17 CLOSED THEN RETURN TRUE " TchO/R Open"
90 IF TIME LEFT THEN RETURN TRUE "Move Open"
100 RETURN FALSE "Stationary"​

P39 – CLOSE CONTROL
Xref your Window Close DO to this point.
Same timer logic as P38.

10 XFlo = POINT 0|37
20 IF XFlo DOWN THEN SET TIMER 7
30 IF POINT 0|18 CLOSED THEN RETURN TRUE "TchO/R Close"
40 IF POINT 0|15 CLOSED THEN RETURN TRUE "FIRE"
50 IF POINT 0|16 CLOSED THEN RETURN TRUE "RAIN"
60 IF POINT 0|19 CLOSED THEN RETURN TRUE "WrgWind Dir'"
70 IF POINT 0|60 CLOSED THEN RETURN TRUE "Time Off"
80 IF POINT 0|17 CLOSED THEN RETURN FALSE " TchO/R Open"
90 IF TIME LEFT THEN RETURN TRUE "Move Close"
100 RETURN FALSE "Stationary"​

📄 Download Configuration Files:

  • Window.doc (Word Document)
  • Window.pdf (PDF Document)
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Attachments
Tags (2)
  • Find more articles tagged with:
  • 13576
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore