When an Alarm point goes into Alarm, it needs to come up on the forefront.
All versions of I/Net using graphics.
When creating Alarms and the point goes in Alarm but does not come to the forefront and stays on the graphic page.
For the page to come up front when the point goes into Alarm, the following steps needs to be followed:
  1. Select System, Edit Graphic Page.
  2. Open the page that the point is on.
  3. Select the point and Right Click to display the properties.
  4. Select the Automatic Page Display check box.
  5. Close the editor and then save the changes.
NOTES:
In order for the auto pop up feature to function, you will need to have the point masked for messaging. Also set AMT Configuration and Host Masking with the corresponding check boxes.