Automatic DPU Restore

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Automatic DPU Restore
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • Tom_Poovey
    Tom_Poovey
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1538 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Automatic DPU Restore

Picard Product_Support
‎2018-09-10 05:44 AM

Issue

Steps for setting up and configuring an Automatic DPU Restore are needed as well as an explanation on how it works.

Product Line

TAC INET

Environment

  • I/NET Seven 2.11 and above
  • DPUs

Cause

The Automatic DPU Restore feature performs two functions. It assures that Access edits are sent to DPUs and that edits done by the badging system are sent to the DPUs. From the I/NET editor usually if an edit is done, it is sent to the appropriate DPUs. However, if any DPUs are not communicating at the time of the edit the Automatic DPU Restore will perform a DPU Restore/Warm Start when the DPU comes back on line. The Automatic DPU Restore feature configures up to five possible Restore Hosts which will minimize the number of hosts that attempt to send DPU Restore commands when the DPUs come back on line. ID Works is configured to send a message to it’s I/NET host which prompts the host to send its data to the DPUs.

Resolution

How automatic DPU restore works

Since Host Masking is set for supervision, all Restore Hosts know who is online.  When an edit is done that could not be downloaded to a DPU the Automatic DPU Restore program enters the Host number of the designated Restore Host and the address of the off line DPU in its table.  If the designated Restore Host is not on line, the program checks the next Restore Host until it finds one on line and puts that Host number in the table.  If the Restore from local host box is checked for a link, that Host number is entered.  When the DPU comes back on line, all Restore hosts that should be masked to see the message check the table and if its number is in the table for the DPU it performs the  Restore DPU/Warm Start.  The Automatic Restore program runs every ten minutes so any DPUs that have come back on line that need to be Restored and can be are.  The Badging program uses the audit message to trigger a download to DPU using the Automatic Restore program since it is only set up to update the SQL database.  MSDE or SQL Server must be running on the Badging host.

 

How to set up and configure the automatic DPU restore

  1. Open AMT
  2. Select Edit > Configuration
  3. Note the Group 1 Masking Settings
  4. Open I/NET
  5. Select Access > Options


     
  6. Select Group 1 for Audit Trail Messaging. Set up the Audit Trail for Group 1. Note: the masking here must match the AMT Group 1 setting.


     
  7. Ensure that the masking for Audit Trail is set the same as the AMT Configuration. Masking here must match the masking set in Step 2 in the Audit Trail.


     
  8. Select Edit > Host Computer > Network Configuration


     
  9. Choose the links that you want to connect to the Reference Host PC, then choose the Modify button.


     
  10. Verify the Host Number


     
  11. Set up Automatic DPU Restore Function. Please note that #60 is the host number of the Reference Host PC. Check the Local Host Box.


     
  12. Make sure in the I/O Server that the Host Masking for all the links that need to have Reference Host connections are set to match the AMT Masking for Group 1.

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 5381
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of