Arm and Disarm Area with Triple Badging at the Door

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Arm and Disarm Area with Triple Badging at the Door
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • AdamSteele
    AdamSteele

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2298 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Arm and Disarm Area with Triple Badging at the Door

Guinan AdamSteele Guinan
‎2019-05-21 01:05 AM

Issue

Require method on how to Arm and Disarm an Area by Triple Badging at the Door.

Product Line

EcoStruxure Security Expert

Environment

Security Expert

Cause

Require Door to be controlled by a Schedule but also to allow a valid User to override the Schedule with three consecutive valid badges.

Resolution

Required Objects

  • virtual Output - Flag to control area status (v_TB_AreaArmedFlag)
  • Area - Area to control (TB_Inside_Area)
  • Programmable Function - Arms Area when virtual output ON (TB_Inside_Area_Arm_PF)
  • Programmable Function - Disarms Area when virtual output OFF (TB_Inside_Area_Disarm_PF)
  • Schedule - Operating hours of Area (TB_Schedule)
  • Door - Door to control Area status (TB_Entrance_Door)

Configuration

  1. Create virtual Output v_TB_AreaArmedFlag. Set Module Type to Output (PX) and Module Address and Module Output channel to ones that do not exist.
    virtual Outputvirtual Output
  2. On the Reader Expander > Reader 1 tab
    - Set Reader 1 Arming Mode to Toggle Function Output on 3 Reads
  3. Set Reader 1 Function Output to v_TB_AreaArmedFlag
    Reader Expander - ConfigurationReader Expander - Configuration
  4. Under Reader Options section set Allow Reading Opened/Unlocked.
  5. Under Misc Options section set Allow Access When Area Armed
    Reader Expander - Misc OptionsReader Expander - Misc Options
  6. On the Doors > General tab
    - Set Area Inside Door to to TB_Inside_Area
    -
    Set Unlock Schedule to NeverDoor - GeneralDoor - General
  7. On the Options tab under Door Options 2 section 
    - Set Door Lock Follows Inside AreaDoor - OptionsDoor - Options
  8. On the Area > Configuration tab under Schedule set Arm/Disarm Schedule to TB_Schedule
  9. Set Disarm Area When Schedule Starts
  10. Set Arm Area When Schedule EndsArea - GeneralArea - General
  11. On Outputs tab set Armed Output to v_TB_AreaArmedFlagArea - OutputsArea - Outputs
  12. Go to Automation > Programmable Functions and create TB_Inside_Area_Arm_PF
    - Set Type to Area Control
    - Set Mode to NormalProgrammable Function - Arm - GeneralProgrammable Function - Arm - General
  13. Under Area Control tab
    - Set Area Function to 2 - Area Arms on Output Turning On
    -
    Set Output To Check to v_TB_AreaArmedFlag
    -
    Set Area To Control to TB_Inside_Area
    - Save changes
    - Right-click TB_Inside_Area_Arm_PF function and select Start
    Programmable Function - Arm - Area ControlProgrammable Function - Arm - Area Control
  14. Go to Automation > Programmable Functions and create TB_Inside_Area_Disarm_PF
    - Set Type to Area Control
    - Set Mode to Normal
  15. Under Area Control tab
    - Set Area Function to 5 - Area Disarms on Output Turning Off
    - Set Output To Check to v_TB_AreaArmedFlag
    -
    Set Area To Control to TB_Inside_Area
    -
    Save changes
  16. Right-click TB_Inside_Area_Disarm_PF function and select Start
    Programmable Function - Disarm - Area ControlProgrammable Function - Disarm - Area Control
Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (2)
  • Find more articles tagged with:
  • AdamSteele19
  • AdamSteele23
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore