Arm/Disarm for I/NET IAS
  • Arm/Disarm for I/NET IAS
  • Roger_Bently
    Roger_Bently
‎2018-09-06 02:46 PM
I/NET
IAS
Configuration Assistance
Are you in the process of using I/Net as an IAS (Intruder Alarm System) and it is not working as you expect? Meaning that you can read a card, but it does not allow access to the door after the pin and code is entered? There is sequence that needs to be followed to ensure that this works properly:
  1. Program door for equivalent reader and PIN if this feature is used.
  2. Set the ATS for Sec/Pin
  3. Select Features and program these as required
  4. Click OK and close out of that Editor, then select Schedules.
  5. Verify that the features are available and select the ones that will correspond to the ones set up in step 3 above.
  6. Hit OK and exit out.
  7. Press #
  8. Read card
  9. Enter PIN (either enter a leading 0 or press # to complete the string)
  10. Press #, the lights should be blinking red/green at this point
  11. Press 0 (function code entered in the function editor)
  12. Press 1 to Arm or 2 to Disarm
  • TAC INET
  • 3096