Issue
Product Line
TAC IA SeriesEnvironment
- Niagara R2 Workplace Pro (all versions)
- Niagara G3 Workbench (all versions)
Cause
Resolution
Niagara R2 and G3 software will work with any antivirus program that allows unblocked communication to the required ports, services, and files listed below:
Niagara R2 Requirements
- Ports:
- Port 80 (Station communications & Web access)
- Port 3011 (Admin Tool)
- Services:
- Niagara Service (Control Panel > Administrative Tools > Services)
- Files:
- Files in
C:\<niagara r2 release number>\nre\bindirectory
- Files in
Niagara G3 Requirements
- Ports:
- Port 80 (Web access)
- Port 1911 (Station communications)
- Port 3011 (Platform access)
- Services:
- Niagara Service (Control Panel > Administrative Tools > Services)
- Files:
- Files in
C:\<niagara g3 release number>\bindirectory
- Files in
Important Notes:
- The specified Ethernet ports must be open bidirectionally for both TCP and UDP traffic.
- Configure antivirus software to allow or “unblock” these ports, services, and files.