Issue
A Trend chart in TAC Vista Workstation is opened and set to show values for the last 4 months, but not all values are shown in the Trend chart.
Product Line
TAC Vista
Environment
- TAC Workstation
Cause
The Trend chart can display maximum 50 000 values. So if you log often and want to display for example the last 4 months, only the latest 50 000 values will be displayed.
Resolution
There is no way around the 50 000 values limit for the Trend chart. To see all values for the last 4 months you need to create several Trend charts.