All graphics are blank when opened on some PC's
  • All graphics are blank when opened on some PC's
  • Jonas_Brissman
    Jonas_Brissman
  • Benji
    Benji
‎2018-09-06 09:53 AM
When a graphic is opened in WorkStation, the graphic work area is just white. If the mouse cursor is moved over the white area, it is possible that some objects will show.
Detected in SmartStruxure version 1.4.1
WorkStation
This is caused by an issue in the graphics card display driver.
Update the graphics card display driver to the newest version.
Sometimes you will need to refer to the manufacturer of the card, and not the manufacturer of the PC.