Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Alarm Forward and Log settings with enhanced alarm logging causes unnecessary network traffic

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Alarm Forward and Log settings with enhanced alarm logging causes unnecessary network traffic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • Carl_Slack
    Carl_Slack
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1736 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Alarm Forward and Log settings with enhanced alarm logging causes unnecessary network traffic

Picard Product_Support
‎2018-09-06 02:52 PM

Issue

Alarm Forward and Log settings with enhanced alarm logging causes unnecessary network traffic

Product Line

Andover Continuum

Environment

Continuum Workstation

Cause

There has been some confusion about whether to select forwarding and logging on the recipient editor located within the eventnotification editor.

Resolution

In 1.5 and later versions of Continuum, a new alarm engine was introduced. To use the new alarming engine, select the enhanced alarming check box located in the database initialization editor. The enhanced alarming feature will perform both the forwarding and logging of an alarm. If the enhanced alarming feature IS SELECTED, then the forwarding and logging of a specific PC will not need to be checked ***. If enhanced alarming IS NOT SELECTED, then you will need to specify a forwarding and logging workstation.

**IMPORTANT: Intrinsic alarms of type Controller Status, Fault Status and Logon Status still need their corresponding Event Enrollment object configured for logging and/or forwarding as before.

If enhanced alarming, forwarding and logging are selected, there will be no duplication of alarms, but will cause unnecessary traffic on the network. If all three are selected and are on a very busy network, you may experience workstations appearing as offline. This can be intermittent depending on the amount of network traffic generated on your site.

To check the settings of your enhanced alarming features, open up the database initialization editor and select either the server or stand alone button to view your settings. If your setting is not selected and you want to use the new alarming engine then select the feature. Make sure you restart ALL workstations when you change this feature.

In 1.7 and later versions of continuum there is also an enhanced alarm delivery selection. This selection uses Microsoft's Messaging Queuing Service to deliver alarms. This feature allows multiple workstations to share the load of delivery of alarms to the recipients of an eventnotification. Thus reducing the work load of just one workstation to handle the delivery. The enhanced alarm delivery feature, will be best utilized when working with multiple workstations.


Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 2883
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of