Issue
- Guidance is required on how to add and bind SNVTs to a Local Node.
- High bandwidth usage on FT10 LonWorks network causing slow system response
Product Line
EcoStruxure Building Operation
Environment
LonWorks FT10 network
Cause
FT10 network bandwidth utilization is high because server-side objects such as TGML graphics and trends poll points on the LonWorks network at a high frequency. Each poll generates communications on the FT10 segment. When a large number of points are polled frequently, network bandwidth can become saturated, resulting in slow system response. A Local Node can reduce polling traffic by allowing server objects to read values locally while field devices update the Local Node through SNVT bindings.
Resolution
Here is a link to a Quick help Video showing how to set up and bind to a Local node