Access Expert Visitor Management Integrations and port requirements

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Access Expert Visitor Management Integrations and port requirements
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1146 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Access Expert Visitor Management Integrations and port requirements

Admiral Alan_Wood Admiral
‎2022-10-19 05:25 PM

on ‎2022-10-19 05:25 PM


Issue

Port information is needed for Access Expert Visitor Management Integrations

 

Product Line

EcoStruxure Access Expert

 

Environment

Access Expert V3 Hosted

 

Cause

LAN port requirements for each VMS integration

 

Resolution

 

Overview

The VMS connection is an important step to the setup of your VMS. Below is a chart of supported VMS and required ports. This article is valid as of 15 November 2019. It should also be noted that many of the VMS allow for the customization of ports and that is not be accounted for in this article. 

 

Ports

OpenEye

Port

Usage

 80 TCP
2000 TCP

Center/Command Incoming Port

2002 TCP

Video/Image Incoming Port

2003 TCP

Search Incoming Port

9876 TCP

Clip Backup Incoming Port

3100 TCP
4007 TCP

Live Incoming port

80 TCP
443 TCP
3478 TCP
1024-655335 In/Out Range

Outgoing Ports

3001 TCP
4006 TCP

DVR Incoming Port

ExacqVision

Port

Usage

80

excaqVision Web Service (customizable)

8082

excaqVision Web Service - Web Socket (customizable)

22609

exacqVision Client computers communicating with exacqVision servers.

Default port 22609.

 

Milestone

Milestone maintains its own knowledge base with an article on ports.

Management Server service and related processes

Port number

Protocol

Process

Connections from...

Purpose

80

HTTP

IIS

All XProtect components

Main communication, for example, authentication and configurations.

443

HTTPS

IIS

XProtect Smart Client and Management Client

Authentication of basic users.

6473

TCP

Management Server service

Management Server tray controller, local connection only

Showing status and managing the service.

7475

TCP

Management Server service

Windows SNMP service

Communication with the SNMP extension agent.
Do not use the port for other purposes even if your system does not apply SNMP.
In XProtect Advanced VMS 2014 systems and older, the port number was 6475.

8080

TCP

Management Server

Local connection only

Communication between internal processes on the server.

8080

TCP

Management Server

Local connection only

Communication between internal processes on the server.

9000(*)

HTTP

Management Server

Recording Server Services

Web service for internal communication between servers.

9993

TCP

Management Server service

Recording Server services

Authentication, configuration, token exchange.

12345

TCP

Management Server service

XProtect Smart Client

Communication between the system and Matrix recipients.
You can change the port number in the Management Client. 

 

Recording Server service

Port number

Protocol

Process

Connections from...

Purpose

25

SMTP

Recording Server service

Cameras, encoders, and I/O devices

Listening for event messages from devices.
The port is disabled by default.

5210

TCP

Recording Server service

Failover Recording Servers

Merging of databases after a Failover Recording Server has been running.

5432

TCP

Recording Server service

Cameras, encoders, and I/O devices

Listening for event messages from devices.

7474

TCP

Recording Server service

Windows SNMP service

Communication with the SNMP extension agent.
Do not use the port for other purposes even if your system does not apply SNMP.
In XProtect Advanced VMS 2014 systems and older, the port number was 6474.

7563

TCP

Recording Server service

XProtect Smart Client, Management Client

Retrieving video and audio streams, PTZ commands.

8966

TCP

Recording Server service

Recording Server tray controller, the local connection only

Showing status and managing the service.

9001(**)

HTTP

Recording Server service

Management Server

Web service for internal communication between servers.
Note: Every Recording Server service needs a port. Additional ports will be 9002, 9003, and so on.

11000

TCP

Recording Server service

Failover Recording Servers

Polling the state of the Recording Servers.

65101

UDP

Recording Server service

Local connection only

Listening for event notifications from the drivers.

 

Client components (outbound connections)

XProtect Smart Client, XProtect Management Client, Milestone Mobile server, Log Server

Port number

Protocol

Connections to...

Purpose

80

HTTP

Management Server service

Authentication

443

HTTPS

Management Server service

Authentication of basic users.

7563

TCP

Recording Server service

Retrieving video and audio streams, PTZ commands.

22331

TCP

Event Server service

Alarms.

22337

TCP

Log Server

Server Logs (System, Audit, Rule-triggered)

 

Web Client, Milestone Mobile client

Port number

Protocol

Connections to...

Purpose

8081

HTTP

Milestone Mobile Server

Retrieving video and audio streams.

8082

HTTPS

Milestone Mobile Server

Retrieving video and audio streams.

 

DataCollector

Port number

Protocol

Connections to...

Purpose

7609

TCP

Recording Server

Collecting data

 

Avigilon

Port number

Protocol

Connections to...

50080

HTTPS

Server

55080

HTTP

Default Camera Device Port

80

HTTP

Streaming / Configuration

443

HTTPS

Streaming / Configuration

 

Salient CompleteView

Port number

Connections to...

80

 

6970-7225

Completeview Server for cameras using General RTSP/UDP

4242

Data

4243

Command

4250

Config Server

4255

Admin Service

4502-4534

Webserver (optional)

 

Wavestore

The default connect port is 8601. This is configurable.

Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (6)
  • Find more articles tagged with:
  • Access Expert
  • AlanWood22
  • integration
  • ports
  • visitor management
  • vms
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore