Access Expert User Group (Permissions)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Access Expert User Group (Permissions)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1302 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Access Expert User Group (Permissions)

Admiral Alan_Wood Admiral
‎2022-10-18 06:34 PM

on ‎2022-10-18 06:34 PM

Issue

Information for User Permissions using Access Expert is needed

Product Line

EcoStruxure Access Expert

Environment

Access Expert V3 Hosted

Cause

Access Expert User Permissions Overview 

Resolution

Overview

User groups and permission are set by an Administrator to manage and control what aspects of the system an operator has. There are no default user login credentials. The user group (permissions) determines what areas of the software a user can access as well as what type of actions they can execute (i.e. update, delete, etc.).

 

User Groups

A key aspect of the Keep permissions engine is the ability to explicitly Deny a trait or option for an operator. This Deny approach allows Administrators to quickly and easily create a new Permission group like an Administrative level operator but without a specific item.

 

User Group Lists

From the General Configuration tab, click on the Groups icon in the Administrative section. This will open a list of all the Permissions currently available in your system. Every system comes with a single System Administrator permission level and there is no limit to the number of Permissions a single system can have.

 

Adding User Groups

To add a new Permission:

  1. Click “Add Group”.
  2. Assign a Display Name.
  3. Assign a Description. The Description should be concise but also provide enough information about the functionality this role will have.
  4. Add desired Permissions.
  5. Click "Save" or "Save & Close".

***IMPORTANT: The minimum permissions to log in are read on the Instance.

 

Keep Objects

Begin by adding rights to the new Permission Group. Note this process starts with the first available tab at the bottom of the screen which is the Objects.

 

Click Add Permission – This will start the process of building out the rights for this type of operator. A full list of Object Types will be provided at the bottom of this article with the associated Linking options.

Add Permission.png

Key Terms:

  1. Object Type – the type of Keep object to be assigned. Object types follow the menu structure of the Keep system such as Access Levels, Badge Design and Controllers. Selecting the All Types option will provide full access to all aspects of the Keep system.
  2. Create – Allows the user to create new objects.
  3. Read – Allows the user to read the objects.
  4. Update – Allows the user to modify existing objects.
  5. Delete – Allows the user to delete the objects.
  6. Publish – Allows the user to publish events with the object type specified.
  7. Advanced Actions - Allows the user to enable advanced actions for integrations such as HID Origo and Single-Sign On.
  8. Linking – When an object type is selected the Linking column will become active. Each object type has a unique series of possible linking traits. When Linking traits are available, the Linking window will display “…”. By clicking the “…” the operator will be presented with the full list of possible traits that can be Added or Removed by checking the available boxes.
  9. Tags – A keyword applied to a series of objects within Keep to help provide additional separation of permissions. An example: an operator can be provided with Administrative level permission but only for items with a specific keyword.
  10. Applies To – Allows the administrator to limit controls to a specific device or series of devices. When being used simply click the “…” icon and the operator will be presented with the ability to choose the devices needed by clicking the Assign Object. Multiple objects can be added. Once the Assign Object icon is pushed simply start typing in the name of the device(s) needed.
  11. Type – Allows for Granting or Denying rights for the object type in that line.

The second portion of setting up a new Permissions Group is to determine the Event Types that the operator will be able to interact with. Event Types is a very dynamic list because the available options will be determined based upon the integrations deployed on your system.

The Event Types section is focused on the types of messages that an operator will be able to see as well as the type of commands the operator will be able to take.

EventTypes.png

Key Terms:

  1. Application – the specific service associated with an application in the system such as Mercury Controllers, Allegion Locks, Video Expert, Mobile, and LDAP.
  2. Event Types – The specific traits associated with the Application. Each Event Type will be different and the options available will be determined by the integrations deployed on your system.
  3. Tags - a keyword applied to a series of objects within Keep to help provide additional separation of permissions. An example: an operator can be provided with Administrative level permission but only for items with a specific keyword.
  4. Type - Allows for Granting or Denying rights for the object type in that line.

Object Types

Each object type has a unique series of possible linking traits. When Linking traits are available, the Linking window will display “…”. By clicking the “…” the operator will be presented with the full list of possible traits that can be Added or Removed by checking the available boxes.

Object and Link Table.png

Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (9)
  • Find more articles tagged with:
  • Access Expert
  • AlanWood22
  • hosted
  • object permissions
  • object types
  • permissions
  • user group lists
  • user groups
  • user permissions
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore