Access Expert Updating Firmware on an SSC or Mercury Controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Access Expert Updating Firmware on an SSC or Mercury Controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1805 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Access Expert Updating Firmware on an SSC or Mercury Controller

Admiral Alan_Wood Admiral
‎2022-10-17 09:19 PM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:33 AM

Issue

Access Expert SSC and Mercury controllers require firmware updates

Product Line

EcoStruxure Access Expert

Environment

Access Expert V3 Hosted

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

SSC and Mercury controller firmware needs to be updated for a fix or feature change

Resolution

Overview

Mercury Controllers operate based on their firmware version and programmed configuration within Keep. It is necessary to update the Mercury firmware on occasion to ensure the most recent features, bug fixes and security upgrades are on the Mercury panel. 

 

Updating Firmware

Mercury controllers can be updated using the Keep by Feenics software. Before updating the controller, confirm the controller is powered on and connected to a Keep by Feenics instance. It is important to have a stable internet connection throughout the entire firmware update process. The duration of the firmware update will depend on the network bandwidth but typically will take between 5 to 10 minutes for a complete update. Users can issue multiple firmware updates to different intelligent controllers at the same time, but not downstream devices.

 

Updating the Firmware on a Controller

To update the firmware on a controller:

  1. Open the controller page. 
  2. Beside the Version field, click on the "Update Firmware" button.

    FirmwareButton.png

  3. Open the Live Monitoring window and set the priority to 0.
  4. In the Live Monitor, you will see the "Downloading Firmware Event".
  5. Once the controller has completed the firmware update, it will reboot. 
  6. After, close and re-open the controller page to see the updated firmware version.

EP Controller Firmware

The EP Series controller's current version is 1.29.1.633 and was released on 2020/01/31. Due to the controllers being End of Life, no new versions of firmware will be released for the EP series controllers.

 

On-Premise Deployments

Note: On-Premise Deployments are no longer supported. All sites will convert to hosted.


The previous process to upgrade firmware for On-premise deployments (servers managed on-site):
They can have their firmware updated out of band by placing the latest Mercury CRC files in the appropriate directory. Once the files are in place users can proceed with the update steps outlined in this article. The default directory for firmware files can be found at C:\Program Files (x86)\Feenics\Mercury Service\MercuryFirmware. 

Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (7)
  • Find more articles tagged with:
  • Access Expert
  • AlanWood22
  • feenics
  • firmware
  • hosted
  • Mercury
  • ssc
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.