Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Access Expert Otis Elevator Integration with Destination Dispatch

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Access Expert Otis Elevator Integration with Destination Dispatch
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
890 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Access Expert Otis Elevator Integration with Destination Dispatch

Alan_Wood Leader
‎2025-07-29 06:57 PM

on ‎2025-07-29 06:57 PM

Issue

How is the Otis elevator destination dispatch system configured in Access Expert?

Product Line

EcoStruxure Access Expert

Environment

  • Access Expert Hosted V3
  • Otis elevator system
  • Mercury controller LP4502/EP4502

Cause

Configuration steps needed for Otis Destination Dispatch in Access Expert

Resolution

An Otis Elevator Compass Destination Dispatching System model allows the LP/EP4502 to inform Access Expert if a cardholder is allowed and authorized for specific floors.

 

Elevator Control Types in Access Expert

There are 2 main types of Elevator control in Access Expert:

  • Basic - does not track the destination of the elevator and cardholder
  • Destination Dispatch - tracks the destination of the elevator and the cardholder

Licensing & Hardware Requirements

  • License required: FN-DEST-OTISRS
  • Controllers: LP4502 or EP4502 Mercury
  • Recommended Adapters:
    • LP4502: Micro-B USB adapter (Pluggable USB2-OTGE100)
    • EP4502: USB 2.0 adapter (Pluggable USB2-E100

Hardware Setup:

  1. Connect the USB adapter to the controller and connect the Ethernet cable for the NIC2 to the Otis network.
  2. Log in to the controller page and navigate to the Network page
  3. Under Interface 2 (NIC2), select Static IP
  4. Type 192.168.50.250 in the IP address field.
  5. Type 255.255.255.0 in the subnet mask field.
  6. Click on Accept at the bottom of the page.
  7. Navigate to Apply Settings.
  8. The controller should reboot to apply the changes.

Mercury Controller Configuration

Ensure the following routes are configured in the Mercury Controller web interface.

LP4502 Configuration Manager.png
Feenics Setup

  • From the Controller Page in Feenics:
    1. On the LP/EP4502 controller page, navigate to the "Destination Dispatch" Tab, located on the bottom of the page.
    2. Select Otis.
    3. Update the floor offset to reflect your Otis setup. The offset must be greater than or equal to 0. Make sure to take into consideration this offset when assigning elevator floor access.
    4. Enable "Has front and rear floors" if your Otis setup has front and rear floors.  Make sure to take into consideration this flag when assigning elevator floors access.
    5. Enable the "Primary Otis controller" option.
    6. Press Save.
    7. Issue a "Push Controller Database" command.

       4502 Elevator Type.png

      Note: The Otis Destination Dispatch Systems can only support one EP/LP4502. In order to support multiple EP/LP4502’s, a Primary and Secondary needs to be configured. The Primary EP4502 will manage communications to the Otis DDS. Communications between the Otis DDS and the Secondary EP4502’s will have to go through the Primary EP4502.

 

  • Reader Page:
    1. On the reader page, navigate to the "Elevator" tab and select "OTIS Destination Dispatching" as the Elevator Type.
    2. In the Dispatch IP enter the DEC (Destination Entry Computer "Touch screen or Keypad") IP address.
    3. For the Elevator Dispatch Mode, select the desired mode. You can hover over the tool-tip to read a description of the mode.

      Reader Modes.png

    4. If desired, select an Override Elevator Access Level. This will allow a set of floors to be public during defined schedules.

    5. Press Save.

    6. Look for an "Otis DEC {Reader} is Online" event in Live Monitoring that reports the controller communication with the DEC.
      elevator type and dispatch selection.png
      The controller will report "Otis DEC {Reader} is Offline" if the communication between it and the DEC drops.

  • Person Page:
    1. On the person page, navigate to the "Destination Dispatch Settings" tab.
    2. On the "Otis Settings" tab, click on "Add Otis Setting".

      Otis Setting.png

    3. Select the Otis controller and press OK.

    4. Select a Default Floor and Floor side. This floor will be served when a DEC is set to Mode 1.

    5. Select User flags. Note that Standard and ADA are mutually exclusive.
      Otis CH Flags.png
      Cardholder Flag selection descriptions:

      • Standard - Standard access, speed and features.

      • Disability - When checked, this indicates the cardholder has a disability. The Otis system recognizes this indicator and cab be set up to provide special accommodations (such as dispatch an adjacent car, extended time to board an elevator car, provide audible announcements at each floor).

      • VIP - When checked, this indicates the cardholder is a VIP. The Otis system can be set up to dispatch an empty elevator car that runs non-stop to the destination floor.

      • Vertigo - When checked, this indicates the cardholder experiences vertigo. The Otis system can be set up to accommodate this passenger by not dispatching them to a glass elevator.

      • SplitGroup - When checked this indicates the cardholder belong to a split group. The Otis system is set up to recognize this person as belonging to a separate group of passengers who use a separate elevator car(s) that is not used by the general population (such as service elevators where technical or service staff do not mix with regular guests).

      • Vertigo2 - no description 

      • CartSvc - no description

      • CIMOverride - Compass Inter-floor Matrix override. This overrides the segmentation used to place certain tenants into certain elevators.


Technical Notes

  • DECs must be represented by readers which can be connected to "fake" downstreams such as the MR52.
  • The Cab used will be sent by the Otis system to Feenics upon access granted and displayed in event data.
Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (5)
  • Find more articles tagged with:
  • Access Expert
  • AlanWood25
  • destination
  • dispatch
  • elevator
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore