Access Expert Mercury Downstream Controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Access Expert Mercury Downstream Controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1574 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Access Expert Mercury Downstream Controllers

Admiral Alan_Wood Admiral
‎2022-10-20 08:25 PM

on ‎2022-10-20 08:25 PM

 


Issue

Information needed for using Mercury downstream controllers with Access Expert

Product Line

EcoStruxure Access Expert

Environment

Access Expert V3 Hosted

Cause

List of Mercury downstream controller and configuration information

Resolution

Mercury Downstreams 
 

Overview

Mercury controllers are an open architecture controller made by Mercury Security. Access Expert supports the series 2 and series 3 SIO boards.

 

Controller Equivalent    Features

FN-RIM1 MR50

Single-card reader interface panel and supports Wiegand, clock and data, magnetic stripe, F2F, Supervised F2F, OSDP, keypad, and biometrics reader technologies.

FN-RIM2 MR52

The MR52 is a dual-card reader interface panel. Each unit can connect two card readers, eight general-purpose input monitor points and six control relays to any Mercury EP series intelligent controller.

FN-16IN MR16IN

The  MR16IN interface panel can support 16 general-purpose input circuits and two dedicated programmable relay outputs.

FN-16OUT MR16OUT

The MR16OUT interface panel provides 16 general-purpose outputs as Form C relay contacts.

FN-MR51e MR51e

The MR51e is a single-door, network-ready interface panel.

 
  Adding Downstreams to Access Expert
  1. Disconnect the power supply from the downstream and the controller.
  2. Set the RS485 jumper to the 2 wire position.
  3. Wire the RS485 communication from the downstream to the controller.
    1. Downstream Controller
      TR+ CLK/Data1
      TR- DAT/Data0
      GND GND
  4. Apply power to the downstream and the controller.
  5. In Access Expert, from the top bar menu (located at the top left corner of the screen) click on the ‘View All Hardware’ button to open the 'Hardware tree'.
  6. In the 'Hardware Tree', double click on the controller or right-click and select ‘Open’ top open the controller page.
  7. Alternatively, click on the 'Hardware Provisioning' tab (located a the top of the screen) to open the menu.
  8. Click on the 'Controllers' icon(located to the left of the 'Hardware Provisioning' menu to open the 'Controllers' page).
  9. Double click or right-click and select 'Open' on the controller, to open that controllers 'Controller Configuration' page.
  10. Click on the ‘Add downstream’ button (located at the top of the controller page) to add a downstream.
  11. From the drop-down menu, select the appropriate downstream model.
  12. Enter a unique ‘Display Name’ for the downstream.
  13. Set the ‘Panel Address’ of the downstream.
  14. Example: To set devices address to 3, DIP switch 1 and 3 must be ON and 2,3 and 4 OFF and 'Panel Address' in Access Xpert must be set to 3. The DIP switches on the downstream must match the ‘Panel Address’ in the 'Downstream Configuration' page.
    Note: DIP switches 1 through 5 sets the device address of the downstream and is binary.
    DIP switch 1 = 1, DIP switch 2 = 2, DIP switch 3 = 4, DIP switch 4 = 8, DIP switch 5 = 16
  15. Confirm that DIP switch 6 and 7 are in the ON position to enable for 38.400BPS communication.
  16. Leave DIP switch 8 in the OFF position.
  17. Click on the ‘Save’ button (located at the bottom of the page) to apply changes to the downstream.

 

Downstreams are added to Access Expert from the Controller page. When adding a downstream, you will need to select the downstream type from the drop-down list. If the downstream you are trying to add does not match one of the types listed, it is either not supported on that port or not supported by that controller.

 
AddDownstream.png
 
Downstream Addressing Chart

DownstreamAddressing-baud.png

 
 
Common Issues

Issue                                             Solution

The EP/LP1501 has no SIO port The EP/LP1501 uses the CLK and DATA on Reader 1 to communicate to downstreams. This means that if you are leveraging a downstream device, the EP/LP1501 only supports 1 onboard reader.
My MR52 is toggling on and offline.

The MR52 has a conflicting address with another downstream. Confirm your dipswitches are set to the correct address.

Addressing is done on dipswitch 1-5 and baud rate is set on dipswitch 6 and 7 (suggested both on). Dipswitch 8 should always be off.

J3 - The jumper for 2 wire and 4 wire RS-485 also needs to be set. By default is set to 2 and should not need changing but this does happen.

J5 is the Termination jumper that needs to be set on the last unit in the series.

My MR51e is programmed for Static IP but won't connect

Check the dip switches on the board. Make sure the dip switches are set back to static IP mode after programming.

Check to make sure the static IP address programmed in is valid.

Make sure the Downstream can be seen by the controller.

My downstream will not come online but my other downstream did.

If you have a Mercury downstream on the same port as an Engage Gateway, the Mercury downstream will not be able to come online. Engage Gateway's and Mercury downstreams cannot share a port.

Confirm the addressing on your downstream is correct. 

My downstream device says "Timeout"

This is due to incorrect addressing or incorrect baud rate set on the downstream.

Dipswitches 1-5 set the address in a binary fashion and dipswitches 6 and 7 set the baud rate. We suggest leaving both 6 and 7 on.

My downstream device says it is in "loader mode" and will not leave that mode

Follow the steps below to correct the loader mode:

  1. Remove Power from the controller and downstreams
  2. Disconnect all downstreams from the controller
  3. Bulk Erase the controller.
  4. Once the controller is powered back on, reconnect the downstream that is in loader mode only.
  5. Reboot the controller.
Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (8)
  • Find more articles tagged with:
  • Access Expert
  • add
  • addressing
  • AlanWood22
  • configure
  • controllers
  • dip switch
  • downstream
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of