Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Access Expert Leave Early Schedule Card Only Configuration

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Access Expert Leave Early Schedule Card Only Configuration
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3258 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Access Expert Leave Early Schedule Card Only Configuration

Alan_Wood Leader
‎2023-10-20 04:14 PM

on ‎2023-10-20 04:14 PM

 

Issue

Schedule a meeting on a day when the site will be closed early. Steps are needed to ensure a door can be configured for 'card only' mode for the meeting.

Product Line

EcoStruxure Access Expert

Environment

Access Expert Hosted V3

Cause

At times it's necessary to schedule a meeting on a day when the site will be closed early. Steps are needed to ensure a door can be configured for 'card only' mode for the meeting and then revert back to the normal schedule or extend the meeting until the end of the standard schedule.

Resolution

Steps to configure a door(s) with a schedule using holidays and 2 T&Ps to temporarily place the door in Card Only mode and then revert back to the standard schedule. In this example, the standard schedule Unlocks the door from 8a-5p.

StandardSchedule.png

 

  1. Create a Holiday (Early Meeting) for the meeting date and ensure a Holiday Group Membership is selected

    LeaveEarly Holiday.png

  2. Configure a schedule(Leave Early) for the meeting date(s) and length of the meeting.
    Select the Holiday Group in this example named 'Early Meeting Test' in the far right drop-down.
    The Holiday Group is needed for this to work.
    Note: The short-duration example was used while testing this multiple times a day.

    LeaveEarlySchedule.png

  3. Configure a T&P (Early Meeting TP) to temporarily change the reader mode to 'Card Only' using the schedule (Leave Early).

    Select the Leave Early schedule and the 'Schedule-Became-Active' Event, the reader mode and the reader(s).

    The "Indefinite" duration drop-down selection worked. The other drop-down options did not work for this schedule implementation.

    EarlyMeetingTP.png

  4. Configure a T&P (Early Meeting Cancel) to cancel the Temporary Reader mode and revert control back to the standard schedule and to Unlock the door.
    Select the Leave Early schedule and the 'Schedule-Became-Inactive' Event, the reader mode and the reader(s).
    Extend the meeting to the end of the standard schedule if needed to keep it in card-only mode.

    EarlyMeetingCancel.png

Testing Results:
At 3:55p the Leave Early meeting schedule became active and the TP changed the reader mode to card only.
* Please disregard the Door held open highlights in the following snapshots

LiveMonitoringDoorInCardOnly.png

At 4:00p the Leave Early meeting schedule became inactive and the TP canceled the temporary reader mode. The door Unlocked in this example after control was handed back to the standard schedule.

LiveMonitoringDoorRevertsToUnlocked.png

Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (5)
  • Find more articles tagged with:
  • AlanWood23
  • early meeting
  • mode
  • reader
  • schedule
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore