Access Expert LDAP/AD Integration agent unable to connect

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Access Expert LDAP/AD Integration agent unable to connect
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2776 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Access Expert LDAP/AD Integration agent unable to connect

Admiral Alan_Wood Admiral
‎2023-07-05 09:24 PM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:32 AM

Issue

Access Expert LDAP agent unable to connect to Instance

Product Line

EcoStruxure Access Expert

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Environment

  • Access Expert V3 Hosted
  • LDAP agent installed OnPrem on-site server (Not the appliance installed by Feenics)

Cause

LDAP agent cannot connect because the Username/PW may be stored in a registry that is no longer valid

Resolution

  1. Double-check the site setup documentation records that the Username/PW combination is correct
  2. Run the SEQ Log and see if there's an entry that indicates that the 'Ldap agent is not able to connect to the instance'

    SEQ log unable to connect to instance.png
    Note: Earlier versions of the LDAP on-site installer did not remove all registry entries including username/pw, so an older username/pw combination may be used instead of an updated combination. 

    If the username or password was changed at some point or if alternate combinations were used for troubleshooting then an incorrect combination could be used by the LDAP agent to connect to the instance and it cannot.

  3. Check the login to Access Expert with one of the LDAP username/password combinations and if there are 2 (Users) listed in Access Expert, delete the username/pw combination that does not work in Access Expert.

  4. Regedit Backup and old Username/PW deletion

    • To obtain a registry backup just in case before deleting an entry:

      https://support.microsoft.com/en-au/topic/how-to-back-up-and-restore-the-registry-in-windows-855140a... 

    • It is suggested to back up the entire Feenics.Keep.ActiveDirectory.Service subkey

  5. Open regedit and delete the imagepath subkey

    • Windows Start/Run> regedit

    • Locate the following registry key:

      HKEY_LOCAL_MACHINE\SYSTEM\ControlSet002\Services\Feenics.Keep.ActiveDirectory.Service

    • Right-click on the ImagePath subkey and select 'Delete'

    • Only delete this subkey, not the other

      LDAP Registry Entry.png

  6. Reinstall the LDAP integration using the media received directly from Feenics or SE Product Support. i.e. Feenics.Keep.Installer.ActiveDirectory.msi
    The most recent version of the install can be found on Feenics site:
    Feenics Keep Active Directory LDAP Installation Media 


    During the installation ensure the tested username/pw combination is used

    LDAP Username PW.png

  7. Verify that the 'Feenics Keep Active Directory Service' starts successfully

    • Go to Start>Run>Services.msc and click Ok

    • Locate the 'Feenics Keep Active Directory Service'

    • Right-click and select Start

  8. Open SEQ Log and verify that the Ldap agent is able to connect to the Instance.

    The SEQ entry at the top of this article 'Ldap agent is not able to connect to the instance.' should no longer appear in the SEQ log. The following entry should be there instead.

    Seq Log AD query entries.png

  9. Verify that the Access Expert Windows User(s) can now be used login to Access Expert

Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (10)
  • Find more articles tagged with:
  • Access Expert
  • active directory
  • ad
  • AlanWood23
  • AlanWood24
  • instance
  • ldap
  • ldap agent
  • login
  • not able to connect to instance
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore