Access Expert Kone Elevator Integration

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Access Expert Kone Elevator Integration
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1488 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Access Expert Kone Elevator Integration

Admiral Alan_Wood Admiral
‎2022-10-17 09:29 PM

Issue

Information is needed about the Access Expert Kone Elevator Integration

Product Line

EcoStruxure Access Expert

Environment

Access Expert Hosted V3

Cause

Kona Elevator integration information 

Resolution

Overview:

Destination Dispatch is a licensed feature for Access Expert and used when customers are modernizing
their elevator systems or deploying newer ones which do not utilize the relay-based approach for floor
control and selection. Within Access Expert, 3 different elevator platforms are supported which include
Otis, Kone and ThyssenKrupp. For this document, we will focus on a KONE deployment. It is important
to note that a single Access Expert can support multiple integrations at the same time.
The KONE integration supports up to 128 total floors of control. When using front and rear entry points
within the elevator cabs), each entry point is considered a separate destination. This means a 32-
story building using front and rear entry points will result in 64 individual destinations.

 

A KONE protocol was created so that the LP controllers can manage access for the KONE Elevator Group Controller. Mercury will support configuration for Destination Operation Panels (DOPs), Car Operation Panels (COPs), and turnstiles. This feature is supported on the LP4502, and EP4502. The support for KONE Elevators was added in firmware 1.25.5.

 

Prerequisites:
1. Access Expert System
2. KONE Destination Dispatch License - FN-DEST-KONERS

3. Appropriate Reader Licenses
4. AX-LP4502
5. Coordination with the Elevator Contractor

A KONE Elevator Destination Dispatching System mode was created within Access Expert so that the
LP4502 intelligent controller can inform a KONE DEC (Destination Entry Computer, E.g. touch screen or
keypad) allowed and authorized floors for a cardholder. This feature is only supported on the LP4502.

Note: Other Elevator Destination Dispatch integrations i.e. Thyssen Krupp and Otis use the 2nd port on the LP4502 controller to communicate with the elevator equipment on a separate subnet.
** The Kone Destination Dispatch integration does NOT support using the 2nd comm port on the LP4502 to communicate with the Kone elevator equipment. If you attempt to do this, you will be unable to connect to the KGCs, and they will not come online.

If you use the Kone elevator simulator for testing, there will not be any response from the KGCs even though you can ping the IP addresses.

 

Controller Page

1. On the LP4502 controller page, navigate to the "Destination Dispatch" Tab.
2. Select Kone.

ControllerPage1.png

3. Enable "Has front and rear floors" if your Kone setup has front and rear floors. Make sure to take into consideration this flag when assigning elevator floors access. It is also recommended to consider the door when creating names. Examples like 2F or 2R are beneficial to system operators.
4. Set the Maximum Cabin Configurations. This is the number of Kone Cabin Access configurations that can be stored on the controller.

ControllerPage2.png

5. Press Save.
6. From the "Add Downstream" dropdown, select Kone KGC under the network port.

ControllerPage3.png

7. Enter the Display Name to be applied to be used. 

ControllerPage4.png

8. Enter the KONE primary KGC IP address and Port.
9. Leave 2005 as the default port number. Press Save
10. Repeat steps 6 to 8 for the Backup KGC.
11. Issue a "Push Controller Database" command.

 

Reader Page

Once the Interface Controller has been saved, add/Navigate to a reader attached to the Controller, and
move to the elevator tab. The Reader does not reside on the KONE KGC downstream. The KGC
downstream is only used to configure the controller with the Primary/Backup KGCs. The readers must
be on the regular Mercury downstream modules or attached to the LP4502. Because of this, the
actual reader setup is similar to a regular door/elevator deployment with the addition of new settings
on the Elevator Tab.
Once the Elevator Type is set to Destination Dispatch, a series of settings will be enabled and
displayed. You will be presented with a WARNING Message when the Elevator Type is selected. This
message is normal and you should select YES.
1. On the reader page, navigate to the "Elevator" tab.
2. Select "Kone Destination Dispatching" as the Elevator Type.

ReaderPage1.png

3. Select the Kone Operation Type. Please note that Kone does not support mixing Remote Call Giving
Interface (RCGIF or turnstiles) with Destination Operation Panel (DOP) and/or Car Operation Panel
(COP). Only one is
supported at a time.
4. Depending on the Operation Type, specify the fields.
5. If desired, select an Override Elevator Access Level. This will allow a set of floors to be public during
defined schedules.
6. Press Save.


Kone Cabin Access Page

1. Navigate to "Access Configuration" on the Main Ribbon bar.
2. Go to "Kone Cabin Access".

CabinPage1.png

3. Click on "Add Kone Cabin Access".
4. Enter a Display Name.
5. Enter the allowed cabins (up to 255). You can use the following formats to enter values: 1-10,15,16.

CabinPage2.png

6. Press Save.


Person Page

Once the reader has been saved navigate to the person(s) who you want to grant access to the
destination dispatch and select the new destination dispatch tab at the bottom of the page this will take
you to a new Destination dispatch tab.
To add an Elevator user setting, simply select the elevator type you wish to grant access to and click the
add button. You will be prompted to select a controller. If there are no active LP4502 elevator
controllers, then the dropdown will be empty meaning the user needs to add a valid controller.
1. On the person page, navigate to the "Destination Dispatch Settings" tab.
2. On the "Kone Settings" tab, click on "Add Kone Setting".
3. Select the Kone controller and press OK.

PersonPage1.png

4. Enter the Default Floor.
5. Enter the Default Floor Side.
6. Select a Cabin Access
7. Select the Kone Elevator flags to be applied to the person.

PersonPage2.png

8. Press Save. 

*Users must configure the Instance Settings to reflect the correct number of floors.

The Cab used will be sent by the Kone system to Keep on an 'Access Granted' and displayed in event data.

Masks

Kone has Global and Specific Masks that are used when setting schedules. These can be set and cleared by right-clicking on the controller and selecting the appropriate option.

Setting the Global Mask opens the Global Mask Configuration window.

To add a floor configuration, click the "Add Floor Configuration" button, then select the desired floors. From there the options for each floor can be selected by setting the appropriate flags for the floor.

Click "OK" to save the changes.


Other Information:

Each Elevator Manufacturer has specific settings, commands or fields when deploying the Destination
Dispatch integration. The following are specific to KONE:
Supported Reader Types:
1. Destination Operation Panel (DOP) – Destination operation panels are located outside of the
elevator car. Each of these will be configured as a separate reader.
2. Car Operation Panel (COP) – Destination operation panels are located inside the elevator cab.
Each of these will be configured as a separate reader.
3. Turnstile (RCGIF) – Turnstiles are half-height sensor barrier solutions designed for public and commercial buildings and airports. Each turnstile will be configured as a reader and must use a Mercury reader port.

Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (6)
  • Find more articles tagged with:
  • Access Expert
  • AlanWood22
  • AlanWood25
  • elevator
  • Kona
  • Kona Integration
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore