Access Expert Exception Schedule for Specific Dates Example

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Access Expert Exception Schedule for Specific Dates Example
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2568 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Access Expert Exception Schedule for Specific Dates Example

Admiral Alan_Wood Admiral
‎2023-08-07 09:38 PM

on ‎2023-08-07 09:38 PM

 

Issue

Access Expert Exceptions for specific dates using holiday durations with an example

Product Line

EcoStruxure Access Expert

Environment

Access Expert Hosted V3

Cause

Instructions with an example are needed to allow exceptions to the standard schedule for specific dates and times

Resolution

At times it's necessary to have schedule exceptions for meetings or other reasons where the date, day, and time need to be specified outside of the standard 8-5 schedule.

 

In order to configure this within Access Expert use the following method:

  1. Verify the main schedule and check the days and times 

    1 Standard Schedule.png

    Note: Adding a schedule duration(interval) to the main schedule allows exceptions to be added however, they will not be specific to a date. The interval add will be for whatever days are selected going forward. For example, All Monday or all Tuesdays in the future for the time specified.

     

    2 Schedule Interval.png

    The above schedule works normally from 8AM - 3:45PM and for all Thursdays going forward the door will unlock from 4PM - 4:05PM

  2. To specify a specific date and time for an exception to the main schedule an additional schedule and a holiday group is needed.

    1. Create another schedule in addition to the standard schedule with the days and times needed.

      Example: Wed7-19 & Th7-20 Council (Council Meeting 6-7p)

      3 Added Schedule.png

    2. From the Access Configuration tab, select Holidays and create a holiday for the specific date(s) needed (Start and End Dates) and select the checkbox for Special Date

      Example: 7/19 and 7/20/23 Council Meeting

      4 Holiday Duration.png

    3. Select the Edit Holiday Group Names button and select one of the default groups and edit the name to be descriptive then Save.

      5 Holiday Group Name.png

    4. From the Holiday Group Membership drop-down select the newly added Group just renamed and click Ok and then Save

      6 Add Holiday Group to New Schedule.png

      Note: The exception schedule will not work unless a Holiday Group has been added

      7 Holiday Group Must Be Added.png

    5. Go back to the new schedule that was created earlier and select the drop-down under Always Active On. Select the checkbox next to the Holiday just created and Click OK then Save.

      8 Adding Holiday Duration to New Schedule.png

  3. A completed schedule with Wednesday and Thursday exceptions that have 7-19 & 7/20/23 specified as holiday durations.

    9 Completed New Schedule with Exception.png

    This will unlock the door during the normal schedule 8-5p

    Lock the door from 5-6p

    Unlock the door from 6-7p for Wednesday and Thursday 7/19/23 and 7/20/23

    Lock the door at 7p for Wednesday and Thursday 7/19/23 and 7/20/23

     

    The holiday exception locked at 4:05p up until 6p

    10 Holiday Exception Locked 405-6p.png

    The holiday exception schedule locked the door at 6p

    11 Holiday Exception Unlocked at 6p.png

Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (8)
  • Find more articles tagged with:
  • Access Expert
  • AlanWood23
  • exception
  • exception schedule
  • holiday
  • meeting
  • off hour
  • schedule
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore