Access Expert 'Error in Live Monitoring document while trying to execute initialize' after setting permissions

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Access Expert 'Error in Live Monitoring document while trying to execute initialize' after setting permissions
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
897 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Access Expert 'Error in Live Monitoring document while trying to execute initialize' after setting permissions

Admiral Alan_Wood Admiral
‎2022-10-19 05:22 PM

on ‎2022-10-19 05:22 PM

Issue

 

A site has multiple locations in its instance. The goal is to restrict objects for a User in other locations by using permissions and tags which allow certain objects only for the local instance. The User also requires access to Event History, Live Monitoring and Floor plans.

 

After setting User permissions for specific objects, the object permissions work as expected, however clicking on Event History, Live Monitoring or a Floor plan shows:

'An error has occurred in the Live monitoring document while trying to execute initialize'


Error Live monitoring document initialize.png

Or Access Expert will show one of the following errors depending on which event object was selected:

'An error has occurred in the Event History document while trying to execute initialize'

'An error has occurred in the Floor Plan document while trying to execute initialize'

 

Product Line

EcoStruxure Access Expert

Environment

Access Expert V3 Hosted

Cause

Event-level permissions function differently than object-level permissions

Resolution

User permissions set up with tags to restrict access to other locations will work as expected with objects like hardware, but these restrictions will not work with event objects.

 

The options to accomplish this are:

1. Buy an enterprise license and divide up the sites with their own instance. Each location should be represented by a shared instance with its controllers configured. Those controllers will publish their event to only their instances which can be controlled using permissions. This is the preferred method.

 

2. Allow ALL Type permissions for the hardware and event objects to be accessed. Using this method allows the event objects to work, but allows Users from other locations to access the hardware.

 

Event-level objects use an entirely different mechanism than regular objects. The technology under the hood requires that an enterprise license be used to accomplish event-level permission restrictions.

Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (15)
  • Find more articles tagged with:
  • Access Expert
  • AlanWood22
  • error
  • event
  • event history
  • events
  • execute initialize
  • instance
  • live
  • live monitoring
  • monitoring event level
  • object
  • object permissions
  • tags
  • user permissions
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore