Access Expert Engage Integration with onboard downstream device showing as Unknown and is offline
Select a Country
  • Access Expert Engage Integration with onboard downstream device showing as Unknown and is offline
  • Alan_Wood
    Alan_Wood
Alan_Wood Leader
‎2023-08-10 07:31 PM
on ‎2023-08-10 07:31 PM
When adding an onboard downstream device (Ex. LP1502) with 4 Engage wireless gateways installed the onboard downstream device shows as 'Unknown' and will not come online
EcoStruxure Access Expert
Access Expert v3 Hosted
If the onboard downstream controller(Ex. LP1502 - onboard) was not being used prior to commissioning and addressing the Engage Gateways then it is likely there is an address conflict.
  1. Check all the downstream device addresses by going to Hardware Provisioning> Downstreams
    If one of the Engage addresses is 0 then it is likely conflicting with the onboard downstream controller's address 0.
  2. Go back through commissioning the Engage gateway devices and re-address them.
    Before
    After
    Once the gateway devices have been re-addressed not using address '0' they should all come online as well as the onboard downstream controller and it should not show as 'Unknown'.
  • EcoStruxure Access Expert
Tags (5)
  • Access Expert
  • address
  • AlanWood23
  • conflict
  • Engage