Access Expert Docker Image Pull Update Instructions

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Access Expert Docker Image Pull Update Instructions
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1101 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Access Expert Docker Image Pull Update Instructions

Admiral Alan_Wood Admiral
‎2025-06-03 06:46 AM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:31 AM

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Issue

Access Expert uses Docker containers and images for the Bosch and Schindler integrations and at times the virtual machine image(s) need to be updated.

Product Line

EcoStruxure Access Expert

Environment

Access Expert Hosted V3

Cause

Feenics updates virtual machine images which requires an update

Resolution

Feenics may update a Docker image for one of their integrations. 

Note: A Docker software update may be indicated in the bottom right of the Docker Window This is only a software update for Docker and will not update the container image. An image update requires a command to Pull the image down from Feenics. The Docker software update is not required to update the Docker Image. (see yellow highlight in the snapshot below)

New Docker Software Version Available.png

 

Here are the instructions to update the Docker Container Image to the (latest)

Open Docker Desktop for Windows

1. Under Containers, make note of the current bosch service name Ex. AX-bosch-service1

2. Stop the container/service using the stop button

3. Click the Red Delete button above the container

Docker Delete Container.pngClick Delete Forever

Delete Only.png

No container after the deleteContainer Deleted.png

Image still showsImage Still shows.png

4. Delete the Image by clicking on the Red Delete button under ImagesSelect Delete Forever (Image)

Delete Image Only2.png

Image deleted (See below)5. Click on the Blue button 'Search images to run'Image Deleted.png

Type in the following to search for Imagesfeenics/keep-bosch:latest

 

6. Select the 'feenics/keep-bosch:latest' Image and Click PULL

Image Search Pull List.png

You will see the progress of the image downloadingImage Download Percentage.png

7. Click on Containers on the top left - the container will not be there

8. Click on Images and then Click the Play button on the Feenics/bosch entry

Docker Image Play and New Update Available.png9. On the next screen, after selecting Play, select the down arrow next to Optional settingsOptional Settings run a new container.pngEnter the original container name that was noted above i.e. AX-bosch-service1, Click Run

New Container with name RUN.pngYou will see messages from the bosch service startup

Bosch service starup log.png

Although the image is updated and running, you will likely see an 81 exception error in the startup log (see highlight above). Here are some additional steps to finalize this process.

 

10. Check in Windows Services> Docker Desktop Service

One of the updates along the way may have changed the startup type to Manual

Double-click on the service and select Automatic for Startup type

Click Start (to start the service)

Click Ok.

 

11. Open Windows PowerShell in ADMIN mode (standard mode will not work)

Run the following command

 

docker run -d --restart unless-stopped --name feenics-bosch-service --env-file C:\ENV\env-us.txt feenics/keep-bosch

 

If you try to run the command with the same name as the original service, you will receive the following message in PowerShell 

PowerShell ContainerName conflict.png

Successful running of the Power Shell command

Successful Power Shell Docker Command.png

This command ensures Docker runs with the parameters that are stored in c:\env-us.txt

ENV-Us.text Docker configu file.png

12. Click on Containers, and there will be 2 Containers

Select the one that is NOT running and click the Red Delete button

2 Container - delete arrow.png

The Delete Forever prompt comes up, select the Delete forever buttonOne container should remain and should be running

Remaining Container After Delete.png

The panel should be online and communicating

AX New Container Running Log and Panel online.png

13. Test and verify everything is working with the Bosch integration

Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (1)
  • Find more articles tagged with:
  • AlanWood25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore